finding Sq. foot of steam
plumb1pa
plumb1pa Member Posts: 10
I've got some old radiators that I have never seen this shape. Where can I go to get info for steam load?
    Jamie Hall Member Posts: 26,828
    Post a few pictures. One of us may have seen them... or they may be in the book (Every Darn Radiator)
    plumb1pa
  • plumb1pa
  • JUGHNE
    JUGHNE Member Posts: 11,511
    That looks like a hot water system?
  • plumb1pa
    Sorry, steam
  • random12345
    random12345 Member Posts: 504
    edited June 2023
    Bundy Standard radiator made by A.A. Griffing Iron Co in NY. They come in heights of 24", 30", 36", and 42" and have 1-4 rows of loops. https://archive.org/details/bundyradiatorsfo00aagrrich/page/20/mode/2up If you look at the base of each of those, I believe you can just make out the company name. Make sure you have the standard loop and not enlarged. It will impact the EDR. See this: https://archive.org/details/illustrated1890900aagr/page/68/mode/2up
    Both of those have two rows of loops, the second white one you posted is 2 rows of 8 loops (2 x 8), so as an example if it's 36" tall with a standard loop then the EDR would be 48 sq. ft. (p. 22 in the first link).
    Here's another catalog from 1885: https://archive.org/details/AAGriffingIronCo/page/n7/mode/2up
    plumb1pa
  • JUGHNE
    A 2 pipe steam system with air vent on the rad?
    Is there some kind of steam trap on the outlet?
    What keeps the steam out of the return line?
    Two pipe air vent steam. An older system, but it works very well.
    And nothing keeps the steam out of the "return" -- the system is described in The Lost Art.
    JUGHNE
  • JUGHNE
    Thanks Jamie, I just had a brain skip firing on all cylinders.
    I have read about this numerous times.
  • plumb1pa
    Thank you all for your posts. Random12345, thanks for the information.
    random12345