EDR for a Keystone Radiator, Not in book
Mark_72
Mark_72 Member Posts: 53
Need a little help finding the EDR for some Keystone rads . Any help would be greatly appreciated.
    ethicalpaul Member Posts: 8,054
    Pics?
  • Mark_72
    WMno57
    edited June 2023
    I'd just pick a similar looking one of roughly the same size. It will be close enough. Given that the sq. ft of steam value is dramatically over-padded with about 30% extra, definitely round down.
    What a beauty by the way
    Mark_72mattmia2
  • Mark_72
  • tim smith
    tim smith Member Posts: 2,886
    I would go off the rococco 3 column same height. I would feel pretty comfortable with that. Whats up with the 2 valves and steam vent???
    Steamhead Member Posts: 18,179
    Those look like standard column radiators. Measure the distance between the center of one section and the center of the next one. If it's 2-1/2", they're standard, and you can use any column rad chart such as American Rococo or Peerless, or U.S. Radiator Florentine or Triton.
    If the measurement is 2-11/16, 3" or 3-1/4", they might be re-branded H.B. Smith radiators.
    Charts for all these rads are in @DanHolohan 's book "E.D.R.".
    Consulting
    Mark_72
  • random12345
    random12345 Member Posts: 504
    edited June 2023
    @Mark_72 Could you please post a few more pictures of any writing you find? Particularly on the top and bottom tappings on either side. It looks like that says "Assyrian Waten" but I can't be sure. Maybe your other radiators will be more legible?
    Mark_72
  • random12345
    edited June 2023
    @Mark_72 Philadelphia Hardware and Malleable Iron Works Inc. is the manufacturer. Credit goes to Ecorad for helping me figure this out: https://ecorad.ca/en/product/assyrian-cast-iron-radiator-electric/
    Here is the only catalog I could find from 1905 that contains the Assyrian: https://archive.org/details/PhiladelphiaHardwareAndMalleableIronWorksIncCCA90B887/page/n9/mode/2up
    The silver rad in the 4th picture down is a Keystone: https://archive.org/details/PhiladelphiaHardwareAndMalleableIronWorksIncCCA90B887/page/n3/mode/2up Ratings are on the next page.
    Little bit of history about Thomas Devlin who became the owner of the company: files.usgwarchives.net/pa/philadelphia/bios/history/devlin-t.txt
    @Erin Holohan Haskell I think the above catalog can go into the Heating Museum. It is copyright-free.
    mattmia2WMno57PC7060Erin Holohan Haskell
    Interesting. Their Assyrian and Penn radiators had 3-inch section spacing, similar to some H.B. Smith models, but the Keystone and Doric ones used the standard 2-1/2-inch spacing.
    This means the Assyrian and Penn have higher EDR ratings than the usual 3-column rads.
    If you're sizing a replacement boiler, this difference can come back to bite you.
    Consulting
    This is a 2-pipe air-vent system.
    Consulting
    Mark_72
  • Mark_72
    I am doing just that. I went off the J.L. Mott 1906. House built in 1906. I came up with 415.75 sq ft and the boiler to be replaced is 671 sq ft so you once again are wright, it will come back and bite me. So I'll look into the links above and see what I have center to center of section. Any help is always accepted. Thanks
    mattmia2 Member Posts: 15,356
    Make sure your near boiler piping and venting and insulation are right so that it will be balanced and heat evenly even if you are a little low on the boiler output.
    Mark_72
  • Mark_72
    Thank you . The home owner will like to know the history of the rads
    random12345
    edited June 2023
    Wait, what exactly bit you? Are you assuming the boiler to be replaced was the right size? Don't do that.
    Can you share what the difference in EDR is between these two examples?
  • random12345
    edited June 2023
    @ethicalpaul American Radiator Company Rococo 3 column: Assyrian Rad:The EDR difference is more significant for the taller heights apparently. Seven 38" 14 section rads measured at 5 sq ft/section instead of 6 would result in an EDR undersizing of nearly 100 sq ft. That could be problem.
    Mark_72
  • Mark_72
    Not assuming , I'm sizing . What is biting me is I sized to the 1906 J.L Mott chart and now i find that the rads have a different rating then Mott. So my sq. ft . edr has changed from 415.75 sq. ft. to 492.25 sq.ft.. If I stuck to Motts chart it would had been undersized.
    OK thanks, I saw you said "the boiler to be replaced is 671" so I thought you were comparing the size of the old boiler.
    But it wouldn't have been undersized. It would have taken away some of the ridiculously large 30% or 33% "pickup factor".
    Mark_72