FlashShield Supply Sizing Question
cwaz
cwaz Member Posts: 22
      I’m in the midst of dealing with a subpar contractor installing my 125k BTU boiler and wanted to verify wether the supply line he ran is sufficient.  I know it is difficult to give exact numbers without seeing the piping in my house but from what I am seeing on the tables, it isn’t even close.
      I have a one inch line entering the house, which runs for 30’ prior to hitting the tee for the boiler. The tee reduces the line to 1/2” FlashShield CSST. It then runs 18’ to the 125k boiler.
     The gas line then continues to serve a 40k water heater, 20k dryer and a gas range (unsure of the btu at this time)
    Is that 1/2” line enough to operate the boiler correctly?
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,069
    edited June 2023
    Hi, I don’t have easy access to the charts right now, but unless it’s running at a higher pressure, like two psi, half inch is too small.
    Yours, Larry
    Ps. There is a lot more to this.
    Rich_49
    pecmsg Member Posts: 7,026
    125K is a big boiler!
    EdTheHeaterMan Member Posts: 12,036
    edited June 2023
    I believe we answered this one on your other post. 1/2" is not large enough for the sizing of your complete system. Minimum 1" Gastite. minimum 3/4. 1" for iron pipe
    mattmia2cwaz
  • Rich_49
    Rich_49 Member Posts: 2,785
    I realize this discussion is a bit old but this answer would depend upon regulator " wc and supplied pressure . It may very well be large enough
    732-751-1560
    Rich McGrath 732-581-3833