FlashShield Supply Sizing Question
cwaz
Member Posts: 22
in Gas Heating
I’m in the midst of dealing with a subpar contractor installing my 125k BTU boiler and wanted to verify wether the supply line he ran is sufficient. I know it is difficult to give exact numbers without seeing the piping in my house but from what I am seeing on the tables, it isn’t even close.
I have a one inch line entering the house, which runs for 30’ prior to hitting the tee for the boiler. The tee reduces the line to 1/2” FlashShield CSST. It then runs 18’ to the 125k boiler.
The gas line then continues to serve a 40k water heater, 20k dryer and a gas range (unsure of the btu at this time)
Is that 1/2” line enough to operate the boiler correctly?
125K is a big boiler!0
I realize this discussion is a bit old but this answer would depend upon regulator " wc and supplied pressure . It may very well be large enoughYou didn't get what you didn't pay for and it will never be what you thought it would .
732-751-1560
Rich McGrath 732-581-38330