Pressuretrol settings
Ollie_Hopnoodle
Member Posts: 73
Do these Pressuretrol settings look right? Thanks. Burnham in5i
This looks like a 2 PSI max with a .5 PSI cut in. That is not so bad. Does the burner cycle on the pressure? That is the real question. If the system never gets to 2 PSI then you are just fine. If your boiler short cycles, then the 1.5 differential may be an attempt to minimize the amount of cycles.
Thanks, yes this is a standard one pipe system. I don't know if it has been short cycling, it's my tenant's boiler. Seems to be running ok though. The boiler is about 100 sqft bigger than the EDR of the radiators though.0
Cycling on pressure is better than letting the pressure go higher, so if you do find out it is cycling on pressure, just make sure the main venting is sufficient and let it cycle, IMO. I'd even lower the Main setting to 1.5 and the Diff setting to 1.0 so that it would cut out at 1.5 and cut back in at .5
There is no possible good reason to keep firing the burners when the pressure is at a high level like 1 PSI or greater. All you're doing is paying money to build pressure, nothing else.
Keeping it at a steady thermostat setting will minimize the length of calls for heat and reduce cycling too.NJ Steam Homeowner.
That's actually very good news. You may very well find even your oversized boiler runs great with good main venting.
See my sight glass boiler videos: https://bit.ly/3sZW1el0
- 50 Industry Classes