Brass pigtails

Options
RayWohlfarth
RayWohlfarth Member Posts: 1,994

I am trying to find the code that says steam boilers should have brass pigtails instead of black iron for a steam boiler. I looked at CSD1 and the wording is hard to understand

Thanks

Ray Wohlfarth
Boiler Lessons

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 8,864

    Codes hard to understand, imagine! 😅 Could you paste the code here, Ray? I'd love to see it.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • RayWohlfarth
    RayWohlfarth Member Posts: 1,994
    Ray Wohlfarth
    Boiler Lessons
    ethicalpaul
  • mattmia2
    mattmia2 Member Posts: 16,895

    Section g and h. Looks like you can use a ferrous pigtail but it mush have a larger ID.

    ethicalpaulbburd
  • ethicalpaul
    ethicalpaul Member Posts: 8,864
    edited March 2023

    Yeah it seems like it requires 1/4" for non-ferrous and 1/2" for ferrous, both up to 5 feet.

    So that seems to rule out 1/4" steel pigtail. thanks for pasting it!

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,564
    edited March 2023

    I'll check NYS & NYC code, but I know for a fact, inspectors WILL NOT allow them in steel irrespective of what the code says Mad

  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,564

    There's good reason.The splooge really adheres to the Black steel pigtails. If you take one out after not being cleaned in a few years, good luck getting it cleared. I think because brass is non ferrous and doesn't rust, there is much less adherence and clogging. By the way, the new yellow brass pigtails...Stink...thinner, not sqaured up and crooked. I.miss my nice Red Brass ones.. Mad Dog

    Long Beach Ed
  • ChrisJ
    ChrisJ Member Posts: 17,412

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    ethicalpaulMad Dog_2reggi
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,564
    edited March 2023

    ELooks to be high quality. Lab quality, perfectly sqaured up and erect like a Army Private at Attention. I presume they make a straight configuration as well? Is that from Mc Master Catalog? Looks like the we company color. Most plumbers are going to ignore because of the 50 Buck tag, but I wanna try one now. Good find, Bravo! Mad

  • ChrisJ
    ChrisJ Member Posts: 17,412

    Yes McMaster.

    They have straight as well.

    They also have them in brass for around $17 but I have no idea how good they are.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ChrisJ
    ChrisJ Member Posts: 17,412
    edited March 2023

    Keep in mind 316 ss is a ferrous metal. Technically.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    Long Beach Ed
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,994

    Update: I contacted the ASME CSd1 committee for their interpretation. I will post what they say. Not sure how long it will take to respond. I am seeing more boiler mmanufacturers using a water seal manifold instead of pig tails. I think it looks better but I wonder if the 1/4" nipples to the controls can be black iron like in the picture.

    water seal copy.jpeg
    Ray Wohlfarth
    Boiler Lessons
  • JUGHNE
    JUGHNE Member Posts: 11,554

    I build the control trees when possible.

    I use brass or SS for the 1/4" risers.

    Use a couple more crosses than shown above.

    My logic is that if the blk pipe manifold is shown clear by looking thru the crosses then the 1/4" risers would be clean.

    ethicalpaulLong Beach Ed
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,994

    @JUGHNE I agree and prefer the manifolds. Thanks

    Ray Wohlfarth
    Boiler Lessons
    mattmia2
  • TonKa
    TonKa Member Posts: 111
    edited March 2023

    FWIW, provision (i) states "Individual controls are to be piped from the manifold according to the provisions of (g) and (h)." I would interpret that, in the last picture posted by RayWohlFarth, they would have to be no smaller than 1/4 inch brass or 1/2 inch black pipe. Additionally, I would interpret the first part of provision (i) as meaning a short manifold would have to be no smaller than 1/2 inch brass or 3/4 inch black pipe. (

  • RayWohlfarth
    RayWohlfarth Member Posts: 1,994

    @TonKa Im thinking the same thing Thanks

    Ray Wohlfarth
    Boiler Lessons
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,529

    We've been dinged on occassion for building our manifolds in iron. Not very often though….

    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • ethicalpaul
    ethicalpaul Member Posts: 8,864

    They gotta find something, right NESW? And on your installs it's damn hard to find something.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    mattmia2
  • mattmia2
    mattmia2 Member Posts: 16,895
  • ethicalpaul
    ethicalpaul Member Posts: 8,864

    Some things are universal

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el