Aquastat alternatives?
rbphhc
rbphhc Member Posts: 127
edited March 2023 in THE MAIN WALL
Any newfangled ways to set hi/lo limits to trigger a circ pump? I dimly remember using Chinese PIDs and relays back when we had a boiler running on veggie oil...
Digital readouts and precise set points would be nice. Aquastats seem designed for fairly narrow differentials. May need to go 30°f+ here. Thx!
  • dko
    dko Member Posts: 669
    A single delta-t circ like the taco vt2218 using two temp probes
    rbphhcSuperTech
  • STEVEusaPA
    How about some more details. What do you have, what are you trying to accomplish?
    rbphhc
  • rbphhc
    edited March 2023
    Trying to maintain indirect between 140 high and 120 low.
    Indirect is acting as buffer tank for direct DHW storage (NTI S20W 20gal).
    Circ pump is a Taco 006e3, but could be upgraded.
  • rbphhc
    Nice pump. But this is circulating DHW, so needs to be SS, bronze, or composite.
  • rbphhc
    Found this on an older thread:
  • rbphhc
    edited March 2023
    One issue is that the NTI indirect comes with its own temperature probe, but no T-stat (unlike an Amtrol, etc).
    A circulator aquastat (Honeywell, etc) has its own single-wire probe. That could be used if I don't use the NTI sensor.
    Ideally I'm looking for something that can take the 2-wire feed off the NTI probe, that's programmable for hi and low limits, and will trigger the circ pump on and off.
    Sensor link here: https://static1.squarespace.com/static/575837b259827e26b5694200/t/612905859a31560073d3a11f/1630078342517/TASSERON+CABLE+TEMP+SENSORS.pdf
    hot_rod Member Posts: 27,278
    My go-to electronic setpoint control.
    If you want variable speed, the solar differential controllers can be set point, differential and variable speed.
    Data logging BTU metering, etc
    rbphhc
  • rbphhc
    hot_rod said:
    My go-to electronic setpoint control. If you want variable speed, the solar differential controllers can be set point, differential and variable speed. Data logging BTU metering, etc
    Nice dude! Thanks!
  • ratio
    ratio Member Posts: 4,217
    +1 on the ETC, it's cheap & flexible. Also Honeywell T775 series, bigger 'n better. If you're into programming, there's https://www.datanab.com/products/mbus_io12_lcd-fully-programmable-modbus-i-o-device-with-lcd-display. Fun to play around with, I've seen them used in the wild by OEMs.
    rbphhc
  • rbphhc
    Looks like that DataNab thing could handle both circ and recirc duties?
  • ratio
    I don't see why not. You can download the free version of the software, write the program, & even simulate it before you shell out.
    rbphhc