Aquastat alternatives?
rbphhc
Member Posts: 127
Any newfangled ways to set hi/lo limits to trigger a circ pump? I dimly remember using Chinese PIDs and relays back when we had a boiler running on veggie oil...
Digital readouts and precise set points would be nice. Aquastats seem designed for fairly narrow differentials. May need to go 30°f+ here. Thx!
Trying to maintain indirect between 140 high and 120 low.STEVEusaPA said:How about some more details. What do you have, what are you trying to accomplish?
Indirect is acting as buffer tank for direct DHW storage (NTI S20W 20gal).
Circ pump is a Taco 006e3, but could be upgraded.
Found this on an older thread:
One issue is that the NTI indirect comes with its own temperature probe, but no T-stat (unlike an Amtrol, etc).
A circulator aquastat (Honeywell, etc) has its own single-wire probe. That could be used if I don't use the NTI sensor.
Ideally I'm looking for something that can take the 2-wire feed off the NTI probe, that's programmable for hi and low limits, and will trigger the circ pump on and off.
Sensor link here: https://static1.squarespace.com/static/575837b259827e26b5694200/t/612905859a31560073d3a11f/1630078342517/TASSERON+CABLE+TEMP+SENSORS.pdf
My go-to electronic setpoint control.
If you want variable speed, the solar differential controllers can be set point, differential and variable speed.
Data logging BTU metering, etcBob "hot rod" Rohr
Living the hydronic dream1 -
+1 on the ETC, it's cheap & flexible. Also Honeywell T775 series, bigger 'n better. If you're into programming, there's https://www.datanab.com/products/mbus_io12_lcd-fully-programmable-modbus-i-o-device-with-lcd-display. Fun to play around with, I've seen them used in the wild by OEMs.1
Looks like that DataNab thing could handle both circ and recirc duties?
- 129 Chimneys & Flues
- 122 Geothermal
