I hate my steam risers
VRA
VRA Member Posts: 5
Hi, I bought a 4th (top) floor apartment in Brooklyn during summer. Once winter came I discovered the nightmare that is the steam risers that end in my apartment. They hiss like crazy, they’re in very inconvenient places, and the expansion noises wake me up at night. I really want to reduce the height for at least the photographed riser as it blocks a window and I want to put up curtains and it’s in my bedroom and the hissing and expansion sounds wake me. Is this possible? Does it matter if it is cut below or above the radiator? I’m so desperate to get rid of this riser in my bedroom I would be willing to forego the radiator all together and use the heat from the hvac mini split and cut the riser off in the floor with an access panel above it. Please lend me your expertise!!!! Thanks! -Veronica
    EdTheHeaterMan Member Posts: 10,680
    edited January 2023
    Probably not a good idea to mess with a pipe in a building you do not own.
    Depending on the system design, you could ask management to do a little repiping. That vent at the top can be below the floor in most cases. You definitely do not need a 8' pipe for that vent. Perhaps a 8" pipe would work. I wonder if someone read the instructions wrong and put a 8 foot pipe where a 8 inch pipe was all that was required?
  • pedmec
    pedmec Member Posts: 1,224
    most likely put that pipe up high so no one will mess with the vent. i have apartment buildings i took over that tenants would tape over the top of the vents to stop the hissing or leaking. some tenants would even hang their shirts from them.
    Mad Dog_2
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,787
    edited January 2023
    Kind of silly way to pipe that. I'd use two 45 degree elbows to offset it against the wall tight against the window casing if you wanted to retain the heat from it. Or cut it off low, as suggested. Moving or shortening it shouldn't affect the radiator. But, as Ed said, it's really not yours to mess with.
    Mad Dog_2
  • VRA
    VRA Member Posts: 5
    edited January 2023
    Hi, it’s me. I’m the management. It’s a small building of which I am the president and no one else has any idea what’s going on. if I cut it off closer to the floor is there a specific valve you recommend? My contractor installed the ones currently on because the previous owner had them glued shut. Does anyone on this thread work in Brooklyn?
  • ChrisJ
    ChrisJ Member Posts: 16,800
    edited January 2023
    I'm sure someone else will comment regarding the height of that riser...
    But if you have hissing going on it's because you're either holding air back and not letting steam get to the radiators fast enough, or, you're creating an excess amount of steam and building unnecessary pressure. Both mean you're burning money for no reason and unintentionally annoying tenants.
    Both can be fixed, one easier than the other.
    When you have time, can you share some pictures of the radiator vents, the riser vents, the main vents and the boiler and it's piping?
    JohnNYquestion
  • KC_Jones
    KC_Jones Member Posts: 5,885
    I agree with @ChrisJ. I will also elaborate. By your description, none of the problems you describe will be fixed by shortening the riser, other than the window blocking issue. Expansion noise will still exist as shortening will not adjust, nor remove any of the parts making noise. The hissing is excess pressure, inadequate venting, oversized boiler, bad piping, any number of things that don't exist at the riser, but may exist at the boiler. If the boiler is oversized you can keep pressure down with a vaporstat, but that is mainly a band aid for an oversized boiler building excess pressure.
    I full appreciate someone moved it to a ridiculous location at some point, but that is honestly a separate issue from the other you present.
    I'm not sure if @JohnNY does Brooklyn or not, I tagged him for comment.
    2014 Weil Mclain EG-40
    JohnNYLRCCBJ
  • Waher
    Waher Member Posts: 335
    @VRA if you could show us a picture of your boiler controls and the other vents in the basement, odds are we could make recommendations to quiet the system and save you fuel. I don't see a problem with that pipe being shortened closer to the floor. That looks like a Gorton No.1 vent to me and a Gorton No.2 may be quieter, however it is best to address boiler settings and the main vents in the basement first to see the effects before replacing anything else.
    EBEBRATT-Ed Member Posts: 18,129
    Contact @JohnNY or @Mad Dog_2
    mattmia2Mad Dog_2
  • JohnNY
    JohnNY Member Posts: 3,324
    Thank you, @KC_Jones
    JohnNY has field techs in Brooklyn every day.
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • Big Ed_4
    Big Ed_4 Member Posts: 3,232
    edited January 2023
    That standpipe was once the only heat source up there before that radiator was installed . I am 90% certain you don't need it .
    guzzinerdLong Beach Ed
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,642
    I would visit the apartment directly below. If there is no radiator connected to that riser then the riser is the heat source for all the apartments below you. In NYC, this was often done in bathrooms and kitchens because there was no room for radiators in those tiny spaces. If that riser is indeed the heat source for the apartments below then that air vent atop the pipe is serving the whole riser. Without it, there will be no heat.
    See if you can check the apartment below for a radiator. That will help us help you. Thanks.
    Retired and loving it.
    ethicalpaulmattmia2ttekushan_3
  • Bill_Kitsch69
    Bill_Kitsch69 Member Posts: 50
    *VRA, The system must be seen as a whole to properly modify piping. Sometimes what's done 'over here,' affects what's happening 'over there.'
    This may have once been a down-feed steam supply, and someone decided to up-feed. This steam main cum vent standpipe would then if so be intended to quick-vent the riser - which it's doing in any "e-vent", but to build this new intentionally would be a bit goofy.
    Diagnostics requires compiling the facts, and a system overview with photos is the place to begin. Any system history is of value.
    automaticsteam@yahoo.com - Bill*
    Double D
  • JWoodoff
    JWoodoff Member Posts: 10
    In my small Brooklyn building, one of the rooms on each side of the building, the room furthest from the boiler, has two risers. One is inside the wall and feeds the radiators; the other is exposed. They are fed separately from the cellar mains. I believe the purpose was to provide additional heat to that room. I can't say why a single riser with larger radiators wasn't the solution, but I think the condition is original.
    I thought the only reason for noisy air valves is a defect in the valve. We recently had all the building's air valves replaced with Heat-Timer Varivalves. They are completely silent. At various times, the older valves would hiss, indicating they had worn out or were defective in some way. Replacing them with a new valve would solve the problem, unless the new valve was defective, which seems to be a problem sometimes with even new valves.
    Long Beach Ed
  • JWoodoff
    After looking again at the picture, another thought occurred to me. If the steam system was installed after your building was built, which is possible if the building dates from the 1880s or 90s or older, it would have been far easier to have all the risers exposed rather than built into the walls. Perhaps the placement of the riser was just for convenience of installation and there is no separate riser to feed the radiators. The system in my building (1909) was part of the original construction.
  • KarlA
    KarlA Member Posts: 3
    I am a homeowner originally from Northern California who has lived in Westchester County, NY for the past ten years. My trades background stems from earning a college degree in Automotive Technology from a college in my home state and working in that trade for a couple of decades. I joined this site to learn more about boiler based heating systems and the interesting history often presented here.
    My automotive trained eye leads me to believe the radiator was added at some point after the riser was installed in the room, as shown in the photograph. While I have seen some dumb installs in the automotive world and the previous two MCM houses I have owned over the years. I have a hard time believing that a skilled tradesman would choose to install large diameter threaded iron pipe in the manner done to fit the radiator if they had any other choice. The supply pipe with valve coming out of the floor at an angle is the give away for me.
    The other thing that caught my eye in the photo is the curious location of an apparent grounded 20 amp electrical circuit, as indicated by a single NEMA 5-20R 20 amp. 125V outlet. Why that type of outlet and why there?
  • gunn308
    gunn308 Member Posts: 13
    KarlA 20 amp outlet by window for window unit AC
    Double DJohnNYPC7060JakeCK
  • SteamFTW
    SteamFTW Member Posts: 76
    Clearly, neither Frank Gerety (nor John Schultz) was ever in this room. ;)
    I know the OP wants to solve the noise problem. Fortunately, there are HH folks who are close enough to make a housecall, and it's not crazy to think that it might be remedied without needing to look under the floorboards. If it does come to that, however, whoever it is who does take on the project, please post some pictures of what you find. It sure looks to me like the radiator was piped *around* the riser, which would mean the riser was already in the way, albeit perhaps not as tall. There are a dozen (less wonky) ways to have done this. Also, the angle that the supply pipe comes out of the floor tells me there something "interesting" (shall we say) going on. Does the supply actually come from somewhere out of frame on the right? I don't want to derail this thread at the expense of the OP getting the problem resolved. I just want to state (or celebrate) the obvious: atypical scenarios like this on HH are so great--apart from the suffering of the resident, of course--because they give us all an opportunity to share how we approach "what you can't see" (without pulling up a floor or opening a wall) based on "what you *can* see", especially when it's something you've never seen before.
    Fast. Cheap. Good.
    Pick any two.
    gassyman
  • Long Beach Ed
    The riser pipe was likely added before the radiators. At one point, NYC required central heating to replace stand-alone gasoline wall heaters. In some taxpayer buildings, landlords just installed bare pipe risers to satisfy the requirement. This building likely predates 1900, as told by the pressed window molding.
    ttekushan_3
  • reggi
    reggi Member Posts: 527
    ^^^THIS^^^  ..
     Where did the heat come from before they put these risers in?
    Did they have to put in their own steam source or did the City run the District Steam?
    I think her riser is in front of the window because when they installed the system they started on the 1st floor to the side of the window but by the time they were going through the 3rd floor ceiling they realized the building had settled and wasn't plumb and that's where it ended up...
    They did better with the riser for the radiator..
    One way to get familiar something you know nothing about is to ask a really smart person a really stupid question
    CLamb
    I'm wonder if the former owner of that building was a dancer and just wanted a poll in the room to practice her trade?
    guzzinerdCLambSolid_Fuel_Mandelcrossv
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,255
    Yep...you just don't know.... a well-meaning bldg super or shoemaker plumber could have left his mark? Its not often, but I very rarely see plumbing and heating from 80-120 years ago that was shoddily put in, but there were a few hacks running around with a lead pot and Stillsons. This is most evident on Bell & Spigot Cast Iron soil pipe with poured lead joints that were hastily slapped together crooked, skewed and cocked at strange angles. I just saw this. Picture is in my phone Ill try to post it. Mad Dog
    Long Beach Ed
  • JohnNY
    There are also pressure and standing water issues that can cause the valves to make a lot of noise.
    This is the first time I've heard anyone use "silent" as a descriptor when discussing Vari-Valves. Typically, people say they work well but are loud. I'm glad you are having a different experience. You must be running at very low pressure.
    Classes
    Long Beach Ed
  • SteamFTW
    @reggi "...the building had settled and wasn't plumb..."
    Can't see outside the window, so maybe the riser for the radiator is what's vertical, and everything in the room is glued down to keep it from sliding away.
    Fast. Cheap. Good.
    Pick any two.
  • Kickstand55
    Kickstand55 Member Posts: 115
    Could be used for a flag pole or a stop sign. May have to move the window.
    Well, that's apartment living.
    If management will allow access to the boiler room and other apartments, and pictures can be had, options can be considered. Or not.
  • Bob_127
    Bob_127 Member Posts: 5
    I had a large brownstone in Brooklyn and for the top (5th) floor, I replaced the valves with a T with the downstream side set up with vents and the upstream side set up to a new straight valve to the radiator. This was to evacuate the risers faster and would still work if I shut of a radiator. Find out if the riser feeds your radiator and you can to something like that. Tell the landlord that it would help to heat the building. I would NOT do anything yourself. Ask the landlord to do it.
  • lowercanada
    lowercanada Member Posts: 14
    too bad it's not over in the corner....
    Mad Dog_2
  • lowercanada
    edited February 2023
    35 years butchering wood (among other things) and I've never heard "pressed window molding. Cast plaster? I see the egg and dart....but the dark streak might be flaked paint?
    I sure hope that picture was taken at night!
    Mad Dog_2
  • Long Beach Ed
    The design is pressed into a soft wood like poplar or "white wood" as it was called between a set of rollers. It's still made today. Cheap alternative to carving and not as detailed. The plaster stuff was "compo" and is still made today too. This is either one but window casing was usually pressed wood. It was cheapest.
    Mad Dog_2ttekushan_3VRA
  • jblum
    jblum Member Posts: 13
    VRA, Did you find a solution? If not, here are my 2 cents. The top-of-riser air vent on single-pipe steam risers does not need to be at ceiling level. The riser can be cut off 12" above the floor and capped with a nipple to install a quieter riser vent such as a Hoffman 4A. I agree with the person who recommended the Heat Timer adjustable air vent for the radiator. The next part of the investigation is to find out the steam pressure settings for the boiler. This system was designed to distribute steam at 1 pound or less, but many boilers are set up initially at 5 pounds. James Blum PE
    Mad Dog_2VRA
  • VRA
    VRA Member Posts: 5
    edited November 2024
    hi. This isn’t resolved and now that winter is back I’m super annoyed again. Attaching pictures.
    The building each unit has heat from the risers and each riser has a radiator associated. Some of the floor plans differ so maybe the radiators are angled differently to accommodate the space but none the less the radiators are each beside a riser. each unit of the 4 units is about 1600 sq feet and the building has a total of 4 risers. Each unit is one floor for a total of 4 floors above ground floors with the boiler in the basement.
    Notably the hissing is WAY worse in the morning bc the thermostat increases from 68 to 72 degrees at 7am. It seems as though that drastic of an increase is leading to significantly more pressure than the usual heat click ons.
    I have reached out to JohnNy but if anyone else is in the park slope area please reach out! 347-989-6464 Veronica
  • VRA
    VRA Member Posts: 5
    fyi for those concerned about my cheap pressed wood casings, they’re actually 120 year old varnished then painted oak…. They are beautiful and irreplaceable after being stripped.
    PC7060
  • dabrakeman
    dabrakeman Member Posts: 754
    Pressuretrol setting is too high. Set it at 2psi with a 1psi diff. If your thermostat control allows it I would suggest breaking up that morning recovery into at least 2 steps.
    Grallertmattmia2
  • DavidK_2
    DavidK_2 Member Posts: 140
    That is a crazy arrangement!
    My guess is the steam riser was put in after the building was built. The radiators were added later because the riser itself did not provide enough heat. But that is only a guess. I'm not an expert on steam heat, or, the history of your building.
    Lowering the pressure might help. Replacing that air vent might also help. Both can be easily undone.
    But that still leaves the riser sticking up in front of your window. Likely it can't just be cut off and caped. It needs to be vented. And that will required threads. I sure it can be done. I think I'd leave the riser as part of the history of your building.
  • Neild5
    Neild5 Member Posts: 203
    That outlet was probably added for a dedicated outlet for a window AC unit. I have also seen 240V outlets in that same position relative to a window.
    delcrossv
  • delcrossv
    delcrossv Member Posts: 2,183
