Help me keep my old boiler alive and well
Unfortunately it's an area lacking steam specialists so it's been maintained by various local plumbing companies. Checked your find a contractor and it comes up with zero at max range. I'm no expert but I'd love to keep it going as long as possible. I do have a copy of the art of steam heating. Seems to be working well, only one radiator out of the 28 in the building has a small leak that I'll take care of when Spring rolls around. I just insulated the steam pipes in the boiler room, the rest are wrapped with a grey clay-ish wrap. The returns are all bare. The entire craw space (48"-60" high) is pretty warm.
Here are pics, any comments, advice etc are welcome. I really want to tune it and keep it going. thanks
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
Looks like a Vapor system. That Return Trap looks like a Dunham. Can you post a few pics of radiators, also the ends of the steam mains to see what's there?All Steamed Up, Inc.
Consulting1 -
Steamhead said:Looks like a Vapor system. That Return Trap looks like a Dunham. Can you post a few pics of radiators, also the ends of the steam mains to see what's there?
Ok, here are some pics of the 3 sizes of radiators in each apt along with pics of the 4 far corners of the mains from the boiler.
Only found one pressure valve on the main installed near a similar valve on the return (2nd pic). I didn't see any others besides those in the boiler room itself.
Nice old system! Of course take care with the asbestos pipe insulation. Keep it in good condition and there is no need to remove it, unless it is in the way of work which needs to be done. An abatement contractor can repair the deteriorated/damaged mudded pipe elbow insulation (remove and replace, or wrap with new canvas).Author of Illustrated Practical Asbestos: For Consultants, Contractors, Property Managers & Regulators2
Just so your terminology doesn't confuse what people think you're talking about, those aren't pressure valves, they are "main vents"NJ Steam Homeowner.
See my sight glass boiler videos: https://bit.ly/3sZW1el5 -
And those main vents look rather small- how long is each steam main, and what pipe size?ethicalpaul said:Only found one pressure valve on the main installed near a similar valve on the return (2nd pic).
Just so your terminology doesn't confuse what people think you're talking about, those aren't pressure valves, they are "main vents"All Steamed Up, Inc.
Consulting0 -
Steamhead said:
And those main vents look rather small- how long is each steam main, and what pipe size?Only found one pressure valve on the main installed near a similar valve on the return (2nd pic).Just so your terminology doesn't confuse what people think you're talking about, those aren't pressure valves, they are "main vents"
ThanksAlexBryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
That is a pretty busy print shown. Do you have the full set for the building.
There may be a page with only piping shown.
It looked like 2" shown, look for a legend to show what solid, dashed lines represent.
The pipes with the arrows indicate the flow of steam and/or condensate return.
The term 2" pipe is measured on the inside of the pipe. the outside will be almost 2 1/2".1 -
The pipes run approx 50' in one direction and 30' in the other. The original plans specify 1/2" mains with 1" return mains but I'd have to go back under to verify. Not in town today.guzzinerd said:
And those main vents look rather small- how long is each steam main, and what pipe size?Steamhead said:Only found one pressure valve on the main installed near a similar valve on the return (2nd pic).
ThanksAlex
Those mains are bigger than 1/2". I'd guess 2-1/2" but we'd need to verify that.
Regardless, you need more venting. Put one Gorton #2 vent on the shorter steam main. On the longer one, install a tee and put a Gorton #2 AND one of your existing vents on there. This should balance the system and let the steam reach the ends of both mains at about the same time.
For the return lines, put a Gorton #2 on each.
Then watch how much faster the system heats up.All Steamed Up, Inc.
Consulting0 -
JUGHNE said:That is a pretty busy print shown. Do you have the full set for the building. There may be a page with only piping shown. It looked like 2" shown, look for a legend to show what solid, dashed lines represent. The pipes with the arrows indicate the flow of steam and/or condensate return. The term 2" pipe is measured on the inside of the pipe. the outside will be almost 2 1/2".
Went down just now and looks like, measuring od, the return is 1.25" and the main is 1.75". This isn't the original boiler so they may have changed the lines when they put in the Bryant.Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
You can get Gorton #2 vents here:
https://www.supplyhouse.com/Gorton-G2-Gorton-No-2-Straight-Air-Eliminator-3524000-p
What part of NM?All Steamed Up, Inc.
Consulting0 -
Steamhead said:You can get Gorton #2 vents here: https://www.supplyhouse.com/Gorton-G2-Gorton-No-2-Straight-Air-Eliminator-3524000-p What part of NM?
I'm in Silver CityBryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
Get four Gorton #2 vents, and install them as outlined in my earlier post.All Steamed Up, Inc.
Consulting0 -
Steamhead said:Get four Gorton #2 vents, and install them as outlined in my earlier post.
Edit: 4 x #2s ordered and on the wayBryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
With the #2 Gortons on the way should I also fit Wye strainers while I'm at it?
Ed, when looking at that print did you see the work "Kewanee" drawn on the boiler?
Those that I have seen have a pretty high water line.
This replacement would have a much lower water line.
Could affect his returns?0 -
We usually don't. Since the vents are mounted vertically, dirt doesn't reach them unless the system floods.guzzinerd said:With the #2 Gortons on the way should I also fit Wye strainers while I'm at it?
Consulting1 -
It could. But first, let's get him properly vented and see where we are.JUGHNE said:Ed, when looking at that print did you see the work "Kewanee" drawn on the boiler?
Could affect his returns?All Steamed Up, Inc.
Consulting1 -
The print calls out a Kewanee #1745. Yes, high water line.0
Ok. I have the Gorton #2s on the long end of the line. Will see how they do after sun down when it gets cold
Regarding the other side with no valves, not sure how to approach that. Once i expose a section of the main do I need to cut a piece out and rethread a new section for the Gorton? Should I be able to do it within a couple of hours? I don't want to start something that i can't finish before the boiler fires up for the evening.
Are there vents on that main now?All Steamed Up, Inc.
Consulting0 -
Not that i saw but i didn't look at it all. Will go down again tomorrow.
Regarding the new vents. The tenant in the unit above them told me the radiators heated up 35 minutes quicker than usual and is super-happy. I went down and it's nice and quiet, no hissing, leaks, hammers etc.Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
3 -
Went down again this morning and found only one other vent on the return a couple feet away from the boiler shown in the pic. I included a pic of the layout again showing the location of the new Gorton #2s (red circle), boiler (green circle) and second return vent (yellow circle).
Where and when/how should I add the other two Gorton #2s?
See if you can locate the end of the steam main(s) on the left side of that diagram- is there a vent at that location?All Steamed Up, Inc.
Consulting0 -
Steamhead said:See if you can locate the end of the steam main(s) on the left side of that diagram- is there a vent at that location?
OK- you need to pipe them in the same way the others were. Use the last takeoff on that main and dry return.All Steamed Up, Inc.
Consulting0 -
Steamhead said:OK- you need to pipe them in the same way the others were. Use the last takeoff on that main and dry return.
You can probably just take out a section and have combination of nipples and fittings with a union to replace the section of pipe.0
mattmia2 said:You can probably just take out a section and have combination of nipples and fittings with a union to replace the section of pipe.
It depends. Sometimes it will unscrew with some big wrenches used properly, other times it won't. If it won't it is usually easiest to either shatter a fitting with 2 small sledges if it is the right type of fitting or to cut a slot almost to the threads and split the fitting with a cold chisel. It is easier to cut a filling off a pipe than a pipe out of a fitting(although the latter is also possible).2
mattmia2 said:It depends. Sometimes it will unscrew with some big wrenches used properly, other times it won't. If it won't it is usually easiest to either shatter a fitting with 2 small sledges if it is the right type of fitting or to cut a slot almost to the threads and split the fitting with a cold chisel. It is easier to cut a filling off a pipe than a pipe out of a fitting(although the latter is also possible).
Can i try map gas to loosen up the threads or is that a hazard on those pipes?Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
> I was afraid years of steam would make them impossible to remove without cutting no?
Steam is not magic, and steel pipes aren't afraid of it. Rust is rust. But even on my 2" original steam main pipes, I can get most of them loose with a couple 18" or 24" pipe wrenches, a 3 or 4 foot cheater pipe, a wooden board to hold the backup wrench and some swearing. And I'm a weakling.NJ Steam Homeowner.
See my sight glass boiler videos: https://bit.ly/3sZW1el1