Steam boiler drawing
Snowmelt
Member Posts: 1,457
Hey I did a quick drawing for a customer, 175,000 btu with three take off & a drop header too I put down 4 or 5 inch but I think 4 would be good.
Also anything wrong with 2 inch on the return
O k thanks0
Scotty is right. Also. I try not to use elbows at ANY LOW points under the water level so you can drain out and flush the mud-puppy legs. Use a heel tee and boiler drain. Mad Dog1
Under the water line I noticed they replaced a length of pipe with 1 inch just to be cheap. ( it’s about 21 feet ) in my head that should be at least 1-1/2 because of sludge, also give the water some volume0
Thanks mad dog, I forgot the term heel tee I will definitely install those in the corners0
Bet you haven't priced 4" and 5" Ward steam tees and elbows! Have fun, check it out! Scott and Mad Dog saved you thousands.
The 1" return will serve 900 EDR (216,000 BTU) of radiators. You'll look up the radiator dimensions and find the EDR of each, which we hope you did when sizing the boiler. Oversizing a boiler is the worst and most common mistake you can make.0 -
We recently installed a Burnham Steamex 500 that has 4 steam tappings. We blew them right up to 4" and didn't even do a drop header and the black pipe and steam fittings were $4600 bucks. I almost fell over!!!!! Mad Dog 🐕2
Whats cheaper than heel tees is a full tee w a black bushing and I like that because you may need down the line for cleaning out returns or pulling a Hydronic zone off it. Mad Dog1
Hey Dog, how do you get that black plug out after ten years?0
It's probably only the drawing, but just to be picky:The elbow off the header for the equalizer should be the same size as the header. You don't want condensate to pool there. You can use a reducing elbow if you want.0
Pictures, Dawg!Mad Dog_2 said:We recently installed a Burnham Steamex 500 that has 4 steam tappings. We blew them right up to 4" and didn't even do a drop header and the black pipe and steam fittings were $4600 bucks. I almost fell over!!!!! Mad Dog 🐕
Consulting0 -
hole saw and hacksawLong Beach Ed said:Hey Dog, how do you get that black plug out after ten years?
Mr Long Beach Ed, King of The Boardwalk. Blue monster Teflon tape and Metaloc dope. Not too tight..won't leak but comes apart easily in 20 years. Steamhead. I will post. Soon. Mad 🐕 Dog.1
- 116 Geothermal
- 169 Indoor-Air Quality