Steam boiler drawing

Options
Snowmelt
Snowmelt Member Posts: 1,415
edited December 2022 in Strictly Steam
Hey I did a quick drawing for a customer, 175,000 btu with three take off & a drop header too I put down 4 or 5 inch but I think 4 would be good.
Also anything wrong with 2 inch on the return

Comments

  • ScottSecor
    ScottSecor Member Posts: 856
    Options
    Four or five inch pipe is total overkill for 175,000 BTU input.  Weil McLain calls for 2.5" header with single 2.5" riser or two 2" risers.  If you ran two 3" risers with a 3" header (dropped or not) I think it work great.
    Long Beach Edethicalpaul
  • ScottSecor
    ScottSecor Member Posts: 856
    Options
    Two inch return sounds like overkill as well.  Nothing wrong with it, but we typical see two 1.25" returns on boilers of this size.
    ethicalpaulLong Beach Ed
  • Snowmelt
    Snowmelt Member Posts: 1,415
    Options
    O k thanks
  • Mad Dog_2
    Mad Dog_2 Member Posts: 6,977
    Options
    Scotty is right. Also. I try not to use elbows at ANY LOW points under the water level so you can drain out and flush the mud-puppy legs.  Use a heel tee and boiler drain. Mad Dog
    Long Beach Ed
  • Snowmelt
    Snowmelt Member Posts: 1,415
    Options
    Under the water line I noticed they replaced a length of pipe with 1 inch just to be cheap. ( it’s about 21 feet ) in my head that should be at least 1-1/2 because of sludge, also give the water some volume
  • Snowmelt
    Snowmelt Member Posts: 1,415
    Options
    Thanks mad dog, I forgot the term heel tee I will definitely install those in the corners
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,210
    edited December 2022
    Options
    Bet you haven't priced 4" and 5" Ward steam tees and elbows! Have fun, check it out! Scott and Mad Dog saved you thousands.

    The 1" return will serve 900 EDR (216,000 BTU) of radiators. You'll look up the radiator dimensions and find the EDR of each, which we hope you did when sizing the boiler. Oversizing a boiler is the worst and most common mistake you can make.
  • Mad Dog_2
    Mad Dog_2 Member Posts: 6,977
    Options
    We recently installed a Burnham Steamex 500 that has 4 steam tappings.  We blew them right up to 4" and didn't even do a drop header and the black pipe and steam fittings were $4600 bucks.  I almost fell over!!!!!  Mad Dog 🐕 
    CLambLong Beach Ed
  • Mad Dog_2
    Mad Dog_2 Member Posts: 6,977
    Options
    Whats cheaper than heel tees is a full tee w a black bushing and I like that because you may need down the line for cleaning out returns or pulling a Hydronic zone off it. Mad Dog
    Long Beach Ed
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,210
    Options
    Hey Dog, how do you get that black plug out after ten years?
  • TonKa
    TonKa Member Posts: 104
    edited December 2022
    Options
    It's probably only the drawing, but just to be picky:
     
    The elbow off the header for the equalizer should be the same size as the header. You don't want condensate to pool there. You can use a reducing elbow if you want.
  • Steamhead
    Steamhead Member Posts: 16,856
    Options
    Mad Dog_2 said:

    We recently installed a Burnham Steamex 500 that has 4 steam tappings.  We blew them right up to 4" and didn't even do a drop header and the black pipe and steam fittings were $4600 bucks.  I almost fell over!!!!!  Mad Dog 🐕 

    Pictures, Dawg!
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • mattmia2
    mattmia2 Member Posts: 9,678
    Options

    Hey Dog, how do you get that black plug out after ten years?

    hole saw and hacksaw
    PC7060
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,210
    edited December 2022
    Options
    mattmia2 said:

    Hey Dog, how do you get that black plug out after ten years?

    hole saw and hacksaw
    That's cheating. Use a $5 brass plug.
  • Mad Dog_2
    Mad Dog_2 Member Posts: 6,977
    Options
    Mr Long Beach Ed, King of The Boardwalk.  Blue monster Teflon tape and Metaloc dope.  Not too tight..won't leak but comes apart easily in 20 years. Steamhead. I will post. Soon. Mad 🐕 Dog. 
    Long Beach Ed