Heat loss calculation - what about setbacks?
bslne
bslne Member Posts: 3
edited December 2022 in THE MAIN WALL
If I understand correctly, a heat loss calculation as used for sizing a heating system is just looking at maintaining a steady state. What about a house where the residents want large setback at night or for vacation? Is there a good way to determine the additional BTUH required to bring the space up to daytime temperature in a certain amount of time?
  • Hot_water_fan
    Hot_water_fan Member Posts: 2,241
    You'd oversize it by a bit, which is likely going to happen naturally since the appliance isn't going to be exactly the right size. Remember, the heat loss is on design day - so while a 100% perfectly sized system would struggle to come back from a setback, it would just be on the coldest days. So if you’re 25% oversized on a day with 90% of the heat loss, you’ll have ample capacity. A deep vacation setback might be more challenging. A WiFi enabled thermostat would probably be the most comfortable option.
    Jamie Hall Member Posts: 27,333
    Just to add to @Hot_water_fan 's comment -- it depends a lot on how fast you want to recover. If you are talking a large setback -- say 10 degrees -- and recovering every morning, then the usual slight oversize will probably do. It will take a couple of hours (a sort of ballpark is around 5 degrees per hour for the average sort of residential system). On the other hand, if you are looking at a larger setback, either plan on spending a day or so getting the place back up to temperature or have a way of starting the recovery early.
    There are methods for computing the recovery time and heat required, but they require knowing a good bit more about the structure and its contents than one usually has available -- and unless one is working on a high value or industrial application, not worth the effort involved.
    hot_rod Member Posts: 27,417
    recovery depends a lot on the heating system. Forced air is quick. Concrete slab not so much.
    Hot_water_fan
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,315
    oh course with "quick" forced air, the air will be 70F, but everything will still be cold. For churches, I usually figure about 30% extra capacity for recovery... that keeps it slow enough so the objects get a chance to warm up. Like already said, for 90% of the heating season, you'll have about 60% extra capacity to recover with, so its not really a big issue. Besides if your structure drops 10F overnight during a typical winter day, then the structure probably needs some thermal upgrades.