Heat loss calculation - what about setbacks?
bslne
Member Posts: 3
If I understand correctly, a heat loss calculation as used for sizing a heating system is just looking at maintaining a steady state. What about a house where the residents want large setback at night or for vacation? Is there a good way to determine the additional BTUH required to bring the space up to daytime temperature in a certain amount of time?
0
Comments
-
You'd oversize it by a bit, which is likely going to happen naturally since the appliance isn't going to be exactly the right size. Remember, the heat loss is on design day - so while a 100% perfectly sized system would struggle to come back from a setback, it would just be on the coldest days. So if you’re 25% oversized on a day with 90% of the heat loss, you’ll have ample capacity. A deep vacation setback might be more challenging. A WiFi enabled thermostat would probably be the most comfortable option.0
-
Just to add to @Hot_water_fan 's comment -- it depends a lot on how fast you want to recover. If you are talking a large setback -- say 10 degrees -- and recovering every morning, then the usual slight oversize will probably do. It will take a couple of hours (a sort of ballpark is around 5 degrees per hour for the average sort of residential system). On the other hand, if you are looking at a larger setback, either plan on spending a day or so getting the place back up to temperature or have a way of starting the recovery early.
There are methods for computing the recovery time and heat required, but they require knowing a good bit more about the structure and its contents than one usually has available -- and unless one is working on a high value or industrial application, not worth the effort involved.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
oh course with "quick" forced air, the air will be 70F, but everything will still be cold. For churches, I usually figure about 30% extra capacity for recovery... that keeps it slow enough so the objects get a chance to warm up. Like already said, for 90% of the heating season, you'll have about 60% extra capacity to recover with, so its not really a big issue. Besides if your structure drops 10F overnight during a typical winter day, then the structure probably needs some thermal upgrades.hot_rod said:recovery depends a lot on the heating system. Forced air is quick. Concrete slab not so much.
To learn more about this professional, click here to visit their ad in Find A Contractor.0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements