Rand and Reardon gas boiler
York101
York101 Member Posts: 2
edited December 2022 in Radiant Heating
HELP not sure what to do with wiring. I bought two taco sentry zone valves. But the wiring is confusing.  Do I need a control box just for the zone valves. What a pain, no service number to call. TIA
Any pictures please
    pecmsg Member Posts: 7,064
    What did you have before the sentry valves?
  • York101
    Old style taco valve 571-2. But the old boiler had a 24v place to hookup valves.
    EdTheHeaterMan Member Posts: 12,182
    Zone valve wiring can be confusing. Are you replacing all the zone valves with Zone Sentry OR are you mixing them up in order to get really confused?
    I can help either way.
    @York101 what model number Rand and Reardon boiler do you have?
    @York101... Here is the old taco 571-2 valve diagram. Lets hope this is the way the old valves were wired
    Lets look at only one valve at a time.
    This is a simplified view of what is going on inside the valve actuator
    Now lets look inside the Zone Sentry valve
    By connecting the W/Y terminal to one of the end switch terminals you get identical wiring to the 571-2 wiring. 1, 2, and 3
    Lets look at how to connect it to YOUR existing wires
    Look in the green Zone Sentry illustration to the left of the original 571-2 in the diagram
    See how the thermostat wire that went on #1 of the 571-2 will connect to the C of the Zone Sentry.
    See how the wire from #2 on the 571-2 goes the the W/Y and one of the end switch wires/
    See how the wire from #3 on the 571-2 goes on the remaining end switch wire
    All the same as the 571-2
    If you do not have the original wiring in a photo or have disconnected all the wires and cant remember where to start, send me a Private Message by clicking on my name in this post.
    Larry Weingartenkcopp
    @York101
    How did everything turn out? Was the wiring help successful?