Radiators not heating up
mcp1
mcp1 Member Posts: 86
I recently took out 2 cast iron radiators from the 2nd floor bedrooms of my house and got them refinished. As I took them out, the risers dropped down a little bit. When I reinstalled them I had to raise the pipe at the bottom of the risers in the basement in order for valve to reconnect to the radiators. Now, some of the other radiators in my house are not heating up. This is a single loop system. I feel heat on parts of the pipe in the basement off the loop, but after it elbows up, the pipe is not hot. Could this be a pitch issue. Any suggestions on how to solve this would be greatly appreciated.
    Jamie Hall Member Posts: 26,140
    I hate to ask the obvious -- but did you purge all the air out of the system after it was put back together? Sometimes just bleeding the radiators is enough -- but usually not.
    mattmia2 Member Posts: 13,316
    Is this monoflow where each emitter is connected to a single loop with branches connected with diverter tees or are the emitters piped one to the other in series?
  • mcp1
    Thanks for the quick response Jamie. I am a complete novice when it comes to this. I did not purge the air out of the system nor do i know how. the radiators that i reinstalled are actually heating up well. Radiators in some of my other rooms are not. I'll post a picture of the pipes
  • mcp1
    These are pictures of the pipes that are going to the radiators, which are not heating up. The pipe toward the end of the run before the risers are cold to the touch
  • neilc
    neilc Member Posts: 3,028
    show a picture of a cold radiator, of each end, top of radiator to the pipe to the floor
    known to beat dead horses
  • kcopp
    kcopp Member Posts: 4,576
    I have a feeling this is a steam system. I think there is a droop in the line and it is trapping the steam from getting through.
    JUGHNEmcp1
  • neilc
    let's add a picture of the boiler, floor to ceiling
    ethicalpaul Member Posts: 7,731
    Strictly Steam? :sweat_smile:
  • mcp1
    This is a steam system on a single loop. Here are some pictures of the boiler & the radiators which aren’t heating up.
  • mcp1
    How is the end of that main vented? Is there a return at the end of the main?
  • Chris_L
    Chris_L Member Posts: 345
    Looks like the steam main is just one continuous loop and the return is the pipe next to the copper fill line. I see at least 3 vents on this line. But I don't see a Hartford Loop anywhere.
    As for the OP's problem of the radiators not heating, were all of them working ok before the two were refinished? If so, did the pipes that got lifted in the basement to reconnect those two radiators get put back in their original positions after the two radiators were connected.
    By lifting the riser in the basement the pitch of other pipes may have been affected leading to poor heating in the other radiators.
    mcp1
  • mcp1
    Chris, that’s exactly what happened. How do I find out what the right pitch should be? Previously the radiators were all heating up. As for main vents I have 1 Hoffman #75 & x3 Gorton #2 main vents at the end of the loop.
    Make sure the end of the main keeps sloping toward the boiler so the condensate can get back to the return at the boiler and doesn't block air or steam.
  • Chris_L
    Yes, you have to make sure the steam main is sloped toward the return for its entire length. And you have to make sure all the branches off the main are sloped back towards it.
    I presume you've removed whatever you used to prop up the risers when you reattached the radiators. In addition to checking the pitch of the main, check the pitch of the runouts to the problem radiators in the basement.
    You might also try lifting the problem radiators by placing something under their legs to see if that helps.
    mcp1
  • pedmec
    pedmec Member Posts: 1,224
    listen to the radiator vent to see if it is letting air out. If not, then remove the air vent and listen for air. if you get air out with the radiator air vent removed then you need to make sure your radiator is pitched toward the the radiator valve so any condensate formed in the air vent is allowed to drain out of the air vent. You don't want the condensate keeping the vent closed. If its pitched correctly then replace the air vent. If no air comes out of the radiator with the air vent removed make sure the radiator valve is opened. if if all that checks out then start checking the pitch on the pipes in the basement.
    mcp1
  • neilc
    so these are the rads that are not heating ?
    I'm not so sure anything to do with having to raise supply riser pipes back up to the refinished rads would have anything to do with this, unless shims, or 4 inches of old paint were under the rad feet, blah blah,
    and It's not like you added pipe nipples, you just raised existing pipe back to where it was,
    now if when risers slid down, other laterals and elbows also fell or their hangers loosened , , , ,
    and did not get back to their good elevation, well that's something to check, that the pitch from the main, all the way to where laterals turn up is even and consistently pitching to drain condensate,
    again, I think you say the rads you refinished, and had to reset their risers, are working, cold issues are on other rads, confirm?
    what I do see, or not see, is,
    the white painted rad, its vent is at its top, and that vent should be down lower, 1/2 to bottom third, of far end from supply valve,
    and I can't see that there is a boss there to accept a vent,
    and on the silver rad, I don't see a vent at all,
    I could have been a bit clearer on asking for the rad pics,
    can we see both ends, from the top of the rad to the floor,
    are the supply valves all the way open?
  • mcp1
    Here are those pictures neil.
  • mcp1
    All the valves are open. The pipe that branches off the main loop is hot until it passes an elbow, then it gets cooler & cooler as the pipe goes towards the riser
  • Danny Scully
    Danny Scully Member Posts: 1,462
    You had vari-vents before? You never know, maybe they just failed.
  • BobC
    BobC Member Posts: 5,523
    In general we like to vent the mains fast which you seem to be doing, but vent the radiators slower. Those heat Timer vents are very fast, how open are they? maybe slowing the ones that are heating up fast will encourage the steam to head for the ones that aren't heating.
    It sounds like things were fine till you had those radiators taken out for refinishing, maybe something changed furing that process. You might want to stretch a string along horizontal piping in the cellar ta make sure you don't have any sags in the piping.
    Bob
    3PSI gauge
    mcp1
    Steam is not getting past that elbow. The question is -- why? I'd start at that elbow, and check the pitch of everything very suspiciously, thinking like water: how would water in this pipe at this location get back to the main?
    Is there any possibility that something got into the pipe during the work? A shop towel (it's happened)?
    If worst comes to worst, try disconnecting one of the problem children and pouring water down the supply line -- it should run back, completely freely, to the boiler. Then try blowing on the line (boiler off please!!) -- it should be easy to blow through the line.
    mcp1