Is this a shut off valve? Please see attached picture.
klau1i5
Member Posts: 2
Hi, I'm trying to purge some air out of my hot water heating system and the zone I am trying to bleed has this type of valve and not a ball valve like on the other zone. I have never seen any valve like this before. I just want to make sure it really is a shutoff valve before I do anything with it. Do I just use a screwdriver, and use the slots to turn it off and on? Since I don't think the valve has ever been used before to shut the zone off to purge air from the zone. Can I drain the entire furnace to purge the zone of air?
its a "purge and balance valve" Close the lower valve with a screwdriver put the slot horizontal. Make note of where this valve is set if not fully open (slot vertical) so you can return it to the slot when done. Keep your circulators off while purging
Then take the cap off the upper valve and put a garden hose on it. Open that valve to purge and close to stop purging.
Maintain 12 psi in the boiler when purging by using the fast fill on the water line PRV.
When done purging shut the upper valve and return the lower valve to where it is now set. Remove the hose and install the cap0 -
Thank you everyone for your replies! very much appreciated.
