Water heater as buffer tank
Snowmelt
Snowmelt Member Posts: 1,457
edited November 2022 in THE MAIN WALL
Starting a new thread here…… I’m thinking it would work from what I asked last time.
I had 4 questions……
1 I was going to use the tapping for the pressure relief valve and the drain valve for the primary loop?
2 hot and cold for the heating loop?
3 small heat load of 70,000 btu ( probably smaller) so was just going to increase the 3/4 to 1 inch with a bushing , nipple and bushing ?
4 The original water heater pressure relieve vale is set for domestic pressure, I was going to take it out, should I put one that matches boiler or leave it out ?
    Jamie Hall Member Posts: 27,014
    Make sure there is a pressure relief valve somewhere on the system which matches the pressure rating of the boiler -- typically 20 psi.
  • Snowmelt
    I was ust going to get the numbers off the boilers pressure relief valve. Technically owes it need one because of the one on the boiler,it’s not a flat plate hex.
    Amie what about the other questions
    hot_rod Member Posts: 27,082
    Common tank type water heaters are built to 300 psi , rated and relief valves at 150 psi, 210 F
    a 30 psi valve should be plenty adequate
    I always left the 150 psi T&P valve in place, added a 30 psi when using water heaters as radiant heat source . So it still had temperature runaway protection
    Maybe a drawing of what you are proposing?
    Larry Weingarten
  • Snowmelt
    Here hot rod a simple drawing keyword buffer tank, 2 air separator 1 make up water
    I’d recommend a 2 pipe buffer
    Either use the two 1” element holes
    Or increase the drain port to 1”
    On top connect the two 3/4 connections into 1”
    be sure to remove the dip tube
    Air purger on the boiler supply pipe
    Expansion tank and fill valve connects at the bottom 1” header
    Add a spring check on the supply from boiler to tank
    A drawing with both options
    GGross
  • Snowmelt
    Thanks hot rod, I’m following the diagram but not understanding how the water is mixing in the tanks, I wanted to keep it simplifies. I guess the other question is would the diagram I gave work. It looked to me like it would mix with the hole tank .
    Any idea of the flow rate on the boiler and heating side. I assume the boiler has a circulator inside? Probably moving more flow into the tank than the heating side, gpm?
    So with a two pipe as I show, you get direct to load flow. If it leaves the boiler at 120F, 120F goes directly to the load side.
    In your drawing, the tank is always involved and you will get a blended temperature, so you may need to run the boiler hotter, maybe much hotter to get desired supply to the heating loop. If you knew the flow rates on both boiler and distribution you can calculate that mixed temperature. My suggested piping eliminates the mixing.
    The dip tube on the C top port is probably 1/2" ID, so depending on flow rates you may get some high turbulence in the tank.
    Be sure it is not a "hydro-jet type dip tube with slots, shown on the attachment. Those slotted tubes are intended to stir up the tank to keep minerals from settling out. But you certainly don't want that in a hydronic buffer.
    It is a very subtle piping difference between what I propose and you have drawn, but it does make a big difference in how the tank stores energy for you. Since you are using a buffer, may as well maximize the tank. Piping should be no more complicated or expensive? Same fittings in a different location :)
    The more you can "stack" or stratify the tank, the more useful that volume of water becomes, the longer you can run without firing the boiler.
    If that is the intent?
    Once the heat call ends the boiler recovers and stacks the tank for the next heat call.
    Hydro-Jet dip tube example attached
    Examples of tank stratification attached
    I would prefer to see the expansion tank closer to the boiler if that pump is pumping into the boiler? Same with the air purger, the hottest point will be at the boiler, best air removal opportunity is there.
    MikeAmann
  • JakeCK
    JakeCK Member Posts: 1,502
    Any recommendations on an electric water heater that you have found that works particularly well for this?
  • Snowmelt
    I’m going to redo your 1st diagram so we’re both on same page , I also like what you sent me fig. 3-5/
    I have used all different brands. I found that some of the Lochinvars come with two extra side taps. Maybe model specific and that is what the supplier I dealt with kept in stock. They catered to commercial accounts.
    I bought one scratch and dent from a box store that had side taps, Richmond brand maybe?
    Stubby tanks seem to have side connections in addition to top. Tall would be a bit better for stratification however.
    You might research models online. Also compare to the Boiler Buddy or HTP buffer tanks that are built specifically for that purpose.
    CBRob
  • GroundUp
    GroundUp Member Posts: 2,483
    @hot_rod thank you for that explanation of the 2 pipe system- I'd always struggled to understand it very well. I do have some questions, however- how is the temp controlled? Does one use a sensor in the tank to tell the boiler when to come on or use the normal zone thermostat and just dump unused BTU into the tank during heat calls? If the latter, what purpose does the tank really serve aside from a heat sink to prevent short cycling? If the former, where does one set the sensor? If we want 120* SWT going to the load and set the boiler output at 120* to work with this 2 pipe buffer, we will never achieve 120* in the tank which would never give us 120* output to the load. Could you please touch on this?
    The boiler only looks at the tank as its load, the boiler operating sensors goes about mid point on the tank. It doesn't know or care what the distribution is doing.
    Its only job is to maintain tank temperature. It is hydraulically separated from the distribution loop also. So no pumping conflicts.
    To maximize the tank, you would want to run it up above the required SWT. the hotter the tank, the more useful energy it stores. The longer the boiler off cycle.
    Think of OWF, they have large water content to store and lessen on off cycles. I look at them as a buffer tank that happens to have a fire below or within :)
    With a condensing boiler it becomes more of a trade off. Unless you have tiny micro loads, a fraction of their lowest turndown, rarely would you need to buffer a mod con. And if you run the tank hot, you lose condensing efficiency.
    It depends on what you expect from a buffer?
    It prevents or lessens short cycling most importantly. Piped properly it becomes a hydraulic separator. It a good place for multiple inputs to end up, wood fired, gas fired, maybe solar thermal or any waste heat from a generator perhaps.
    Air and dirt removal to some extent.
    MikeAmann
  • Snowmelt
    Ok here is what i think your doing.
    Tank is heated up by boiler to what ever temp when call for heat.
    The zone takes water fro the tank to the return off the drain valve area back to the boiler , boiler will fire to satisfied.
    On the supply the water will be drawn from the tank because of lease head pressure
  • Snowmelt
    Yikes I forgot this is a condensing boiler I think I need closely spaced tees at the boiler
  • GGross
    GGross Member Posts: 1,777
    The buffer should act as a hydraulic separator and give you primary secondary piping
  • JakeCK
    @Snowmelt I do not believe you would need the closely spaced T's if using a buffer tank. The tank provides the hydraulic separation. That said why do you want to use a buffer with a modcon boiler?
    @hot_rod I did find this one but it is a mobile home tank. I doubt that would matter, however, in this case. It has 6 taps on the side for the elements, hot and cold, t&p valve and drain. And one on top for the anode. Can the dip tubes be removed from side port water heaters? It mentions in the manual about a spiral jet system to prevent sediment build up too. Would the hot and cold ports even be useful in this case?
    https://www.menards.com/main/plumbing/water-heaters/electric-water-heaters/richmond-reg-essential-reg-6-year-mobile-home-electric-water-heater/t2v40-d/p-1444452213419-c-8690.htm
  • Snowmelt
    I posted the last comment without thinking.
    Only reason to do this is because it’s existing, customer is claiming of short cycling
    The tank is maintained hot, always, not just on a heat call. Because if the tank is hot and a heat call comes on, the boiler doesn't fire until the tank temperature drops. It can drop to the lowest possible useable temperature. So the tank could run a 20- 30 even higher delta. Load it to 180F or whatever, pull it down to 150, 120, whatever temperature covers the load. Make sense?
    Even better yet would be to pull the loads off via an outdoor reset control. So then the "exact" temperature is pulled from the tank for the load.
    With a mod con, if you know what the smallest load possible is, and the lowest turndown on the boiler, 17,000 I imagine? Plug it into this formula. Buffer tanks for modulating boilers are much smaller due to the turndown of the boiler.
    If your smallest load isn't below 17K, maybe even below 8,000 btu/hr. I see no reason to even add a buffer tank?? If it short cycles at a 17K output it could be the control is not dialed in?
    Look for a ramp delay function. It locks the boiler at a fixed modulation for the time you determine.
    My Lochinvar has 6 or 7 steps. I have a 15 minute increment set. So it stays at 8k for 15 minutes, which on mild days covers the load. Every 15 minutes it bumps up another 10- 15% output, In an hour it is at 100% if the load has not been covered.
    I also have boost function. If the boiler sees temperature dropping, falling behind the load at it current firing rate, it understands it needs to bump up.
    As mentioned above the tank IS the hydraulic separator. And that is regardless of a 2, 3 or 4 pipe setup.
    MikeAmann
    A great tank for buffer. Usually the dip tube is molded into those nipples you see and the nipple could be removed and a standard nipple installed. i think a company in Tennessee makes most of the water heater nipples and dip tubes. The side nipples usually have a gooseneck plastic tube inside to direct flow. If it has the slotted cuts in the side of the dip tube it stirs the incoming water.
  • Snowmelt
    Hot rod thanks, the last diagram that I sent, is that pretty much what you draw, only other thing was, I think you mentioned a check valve on the supply ?
    All the ups and downs are making me dizzy, but you have the concept :)
    I assume this bottom right hand pipe goes behind the tank, not into the bottom right side of the tank?
    Just be sure you aren't designing a solution for a non existent problem or symptom.
    Is this a 175K boiler or tankless DHW heater?
    I'd sit alongside that boiler for an hour or so on a mild or shoulder season load. Or even a single small zone load and see what the cycle looks like.
    I'm feeling more like a control reprogram may be an adequate fix?
    The industry seems to agree on a 10 minute minimum run time when a boiler fires.
    JakeCK
  • Snowmelt
    Your right the pipe goes around the tank , I’m not a 100% sure but I think it’s a 175,000 Bosch combo , I think minimum fire is 18,000. It’s an existing system that has issues of runaway heat, to many check valves, primary/ secondary isn’t used properly. Transformers all over the place, extra zone valves, then on top of that there is an electric water heater used as a buffer.
  • MatthewPK
    MatthewPK Member Posts: 22
    edited February 2025
    Bumping this great old thread because I plan to try this strategy. How would you handle tank temperature regulation? I'm looking at using a strap on aquastat directly to the steel tank. It seems like inexpensive modern electric water heaters don't have a satisfactory thermostat for this use case. Using a basic aquastat I can target 180 with a 50 degree differential.
    This is the control I like to use. It has a lot of adjustability, nice readout. Other versions from HW and Johnson controls. The sensor against the metal tank jammed under the tank foam insulation is accurate enough.
    MatthewPK
  • mrm
    mrm Member Posts: 1
    I'm new to all this so maybe a stupid question - if the sole purpose of a buffer tank is to add mass/water volume in order to stop boiler short cycling during low demand seasons (spring/fall), can't the tank be piped more simply, i.e. all return water into a top tap on the tank and then all out a bottom tap back to the boiler. Then no added circ pump and controls to control boiler firing based on tank temp, just let existing controls call for heat for a zone and boiler firing continues to be based on boiler thermowell temp. Not as sophisticated as 4 pipe system, and maybe not as efficient, but simpler and still adds thermal mass for short cycling fix. Boiler thermowell temp should rise and fall more slowly since there is more water in the overall system.
  • HydronicMike
    HydronicMike Member Posts: 295
    Buffer on the return.
    It wouldn’t work in the return scenario as you wouldn’t control the temperature going out to the zones. The hottest boiler water would be going out to the zones, satisfying the call for heat and short cycling, with the buffer doing nothing.
    edited August 2025
    a 2 pipe buffer ins not too complex to pipe and adds a lot of features. So comparisons here
    https://www.caleffi.com/sites/default/files/media/external-file/Idronics_17_NA_Thermal%20storage%20in%20hydronic%20systems.pdf
  • SHMA
    SHMA Member Posts: 1
    Thanks for the help. Went and looked at a GSHP system for a friend/house purchase and knew the EWH/buffer wasn't piped the way it should be. I didn't even know if it was possible to make it work but the sketch helped loads. All makes sense now. Thanks Bob! I did a little redraw to fit this system and made it fancy.