Prestige boiler issue

timdelsordo
Member Posts: 1
I have like-warm water to all faucets in my home. All discharge pipes from boiler are almost too hot to touch. Heat in house works just fine. I’m at a loss as to why this is happening. HELP!
0
Comments
-
dhw heat exchanger may need internal cleaning with chemicals. did this happen gradually or all of a sudden?0
-
-
Bad pump for indirect hw tank?0
-
This can happen when a mixing faucet, like a shower valve, is left open and the flow stopped with another valve downstream, such as a handheld showerhead.—
Bburd0 -
Do you have a Prestige Solo (heating only with a sidearm water heater) or Prestige Excellence (combi)?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
My bet is a cross connect between hot and cold. What changed? Did you add a shower head with a shutoff somewhere?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0