Adding pressure to a system with zone valves
joeba
joeba Member Posts: 24
On a system with zone valves on the supply, and the circulator on the return(007 no internal check), do you have to open zone valves? I am assuming no, since the auto-feed has no idea if the zone valves are open or closed
    Jamie Hall Member Posts: 27,200
    No, you don't.
  • joeba
    So I always like to know why. What happens if you do open them? Does it matter?
    Alan (California Radiant) Forbes Member Posts: 4,694
    edited September 2022
    If you add water with the zone valves closed, water will be added through the pump on the return as there is no check valve.
    If say, there is a flow check on the pump, the location of the fill valve in the system will determine the outcome.
    hot_rod Member Posts: 27,276
    The additional water (pressure) will go somewhere- into the boiler, expansion tank, piping, etc.
    Check the expansion tank pre-charge pressure before you add water and occasionally through the years. You need to isolate or remove the tank to do that.