Adding pressure to a system with zone valves

joeba
Member Posts: 24
On a system with zone valves on the supply, and the circulator on the return(007 no internal check), do you have to open zone valves? I am assuming no, since the auto-feed has no idea if the zone valves are open or closed
0
Comments
-
No, you don't.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
So I always like to know why. What happens if you do open them? Does it matter?0
-
If you add water with the zone valves closed, water will be added through the pump on the return as there is no check valve.If say, there is a flow check on the pump, the location of the fill valve in the system will determine the outcome.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
The additional water (pressure) will go somewhere- into the boiler, expansion tank, piping, etc.
Check the expansion tank pre-charge pressure before you add water and occasionally through the years. You need to isolate or remove the tank to do that.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements