B&G control valve elimination
I want to clean up my boiler. I was told by a heating & cooling contractor long ago that my system setup no longer requires the B&G flow control valve. It has started dripping last winter so I want to eliminate it. In handy with the torch and doing the work but not sure if I simply replace the valve with a t? Boiler output comes through the bottom of valve, one side exits to the zone valves and the other to the expansion tank. I’ll upload some photos.
You can replace it with a tee or an ell and move the expansion tank somewhere else. I assume this boiler has a circulator pumping in to it from the return which means it is also pumping in to the expansion tank. The expansion tank would be better on the return before the circulator so the pressure from the circulator isn't pushing in to the tank.0
Looks like you have 2 zones that have zone valves. If that is true you can eliminate the B& G flow check valve and replace it with a tee.0
The boiler does have the circulator on the return side. 2 zone valves and one old school t stat valve. So I’d have to move the expansion tank and solder elbow in place of the B&G…expansion tank before the pump on the return is preferable?0
Could I just leave the tank where it is and sweat the tee in place of the valve?0
I suppose you can get another control valve and keep everything as is. I saw that Ebay has them on the cheap side:
B&L 107018
B&L 107018 free shippingI'm not a plumber or hvac man and my thoughts in comments are purely for conversation.0 -
Thanks for the advice. I’ll sweat a tee in place of the valve.0
Have you had any noise or air problems since the zone valves were installed?
Got a pic from a step back to see them entire boiler piping?
Since you will be draining down it would be an option to move them pump or expansion tank connection. It could be fairly simple to do. A delta P circulator would be a nice upgrade also.
B&G has been explaining to importance of proper expansion tank location for 60 years or so now.
But what do theyn know
Doesn't the one way valve prevent water from pumping into the expansion tank? With a T the expansion tank should probably be moved, no?I'm not a plumber or hvac man and my thoughts in comments are purely for conversation.0
@MikeAmann yes you can move it to the return. In fact, Weil McLain shows it on the return in some of their install drawings1
My boiler has been improperly plumbed for God knows how long and it’s worked fine all these years. Is it the best layout…no but it’s been heating the house for the past 30 + years just fine. So I wouldn’t worry too much about placement unless of coarse you have problems or are installing a new boiler. Just isn’t worth the time & money to most likely end up with the same results.0
Oh manufacturers & suppliers know lots; but their business is to sell stuff. Especially stuff that eventually needs to be replaced. Modern Xtanks is sweet example.hot_rod said:Have you had any noise or air problems
Why not just repack it and not worry about it?
You can repack it by removing the threaded top,
install a new gasket and then open it up fully and
avoid all that extra work.0
- 116 Geothermal
- 169 Indoor-Air Quality