Piston
johnjohn89
Member Posts: 115
Why charge wet bulb and dry bulb when system use piston metering device ? And why txv doesn’t charge by wet bulb and dry bulb ?
As far as I know with a fixed orifice device like a piston you charge by superheat.
With a txv you charge by subcooling because the txv controls superheat, so you can't really charge by it. Personally I watch superheat as well with a txv and adjust the txv if possible to get both superheat and subcooling where they need to be .
Subcooling is really just showing you how much reserve liquid refrigerant you have backed up in the condenser.
because with fixed metering device a greater portion of the refrigerant is used to remove the latent heat plus the sensible heat. so on a humid day your superheat will increase due to the higher latent heat load on the evaporator coil.
with a txv it will just open up to maintain the proper superheat due to the increased load.0 -
ChrisJ said:As far as I know with a fixed orifice device like a piston you charge by superheat.
Ture thanks
Great answer thank u so muchpedmec said:because with fixed metering device a greater portion of the refrigerant is used to remove the latent heat plus the sensible heat. so on a humid day your superheat will increase due to the higher latent heat load on the evaporator coil. with a txv it will just open up to maintain the proper superheat due to the increased load.0