Why charge wet bulb and dry bulb when system use piston metering device ? And why txv doesn’t charge by wet bulb and dry bulb ?
0
Comments
-
As far as I know with a fixed orifice device like a piston you charge by superheat.
With a txv you charge by subcooling because the txv controls superheat, so you can't really charge by it. Personally I watch superheat as well with a txv and adjust the txv if possible to get both superheat and subcooling where they need to be .
Subcooling is really just showing you how much reserve liquid refrigerant you have backed up in the condenser.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment1 -
because with fixed metering device a greater portion of the refrigerant is used to remove the latent heat plus the sensible heat. so on a humid day your superheat will increase due to the higher latent heat load on the evaporator coil.
with a txv it will just open up to maintain the proper superheat due to the increased load.0 -
ChrisJ said:As far as I know with a fixed orifice device like a piston you charge by superheat.
With a txv you charge by subcooling because the txv controls superheat, so you can't really charge by it. Personally I watch superheat as well with a txv and adjust the txv if possible to get both superheat and subcooling where they need to be .
Subcooling is really just showing you how much reserve liquid refrigerant you have backed up in the condenser.
Ture thanks
0 -
pedmec said:because with fixed metering device a greater portion of the refrigerant is used to remove the latent heat plus the sensible heat. so on a humid day your superheat will increase due to the higher latent heat load on the evaporator coil. with a txv it will just open up to maintain the proper superheat due to the increased load.0
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 418 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 160 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 848 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 38 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements