                    Why charge wet bulb and dry bulb when system use piston metering device ? And why txv doesn’t charge by wet bulb and dry bulb ?                
                0                
            Comments
- 
            As far as I know with a fixed orifice device like a piston you charge by superheat.
 With a txv you charge by subcooling because the txv controls superheat, so you can't really charge by it. Personally I watch superheat as well with a txv and adjust the txv if possible to get both superheat and subcooling where they need to be .
 Subcooling is really just showing you how much reserve liquid refrigerant you have backed up in the condenser.
 Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times. 1
- 
            because with fixed metering device a greater portion of the refrigerant is used to remove the latent heat plus the sensible heat. so on a humid day your superheat will increase due to the higher latent heat load on the evaporator coil.
 with a txv it will just open up to maintain the proper superheat due to the increased load.0
- 
            ChrisJ said:As far as I know with a fixed orifice device like a piston you charge by superheat.
 With a txv you charge by subcooling because the txv controls superheat, so you can't really charge by it. Personally I watch superheat as well with a txv and adjust the txv if possible to get both superheat and subcooling where they need to be .
 Subcooling is really just showing you how much reserve liquid refrigerant you have backed up in the condenser.
 Ture thanks
 0
- 
            
 Great answer thank u so muchpedmec said:because with fixed metering device a greater portion of the refrigerant is used to remove the latent heat plus the sensible heat. so on a humid day your superheat will increase due to the higher latent heat load on the evaporator coil. with a txv it will just open up to maintain the proper superheat due to the increased load.0
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements