Refrigerant
johnjohn89
Member Posts: 114
Why increase liquid pressure then lower vapor pressure?0
Isn't that chart usually for confirmation of correct charge, not for charging?0
@johnjohn89
It's all about the refrigeration cycle. Refrigerant vapor is pumped by the compressor (compressors can't pump liquid).
The compressor pumps the refrigerant to a higher pressure and corresponding temperature that has to be a higher temperature than the outdoor ambient temperature (assuming and air-cooled condenser)
When the refrigerant enters the condenser, it is cooled to a lower temperature, giving off heat (by air from the condenser fan blowing across the coil) but stays at the same pressure thus changing from a gas to a liquid.
The liquid flows through the liquid line to the metering device (expansion valve, cap tube or restrictor) which reduces the pressure of the liquid and the liquid "boils" at around 40 degrees F for and air conditioner and then absorbs heat into the refrigerant in the evaporator coil.
It then returns to the compressor and the cycle is repeated.
There are You tube videos that can explain this better than I can. Go to you tube and look up "AC Service tech" and search his videos0 -
charging chart for fixed metering device.0
Ok thank uEBEBRATT-Ed said:@johnjohn89 It's all about the refrigeration cycle. Refrigerant vapor is pumped by the compressor (compressors can't pump liquid). The compressor pumps the refrigerant to a higher pressure and corresponding temperature that has to be a higher temperature than the outdoor ambient temperature (assuming and air-cooled condenser) When the refrigerant enters the condenser, it is cooled to a lower temperature, giving off heat (by air from the condenser fan blowing across the coil) but stays at the same pressure thus changing from a gas to a liquid. The liquid flows through the liquid line to the metering device (expansion valve, cap tube or restrictor) which reduces the pressure of the liquid and the liquid "boils" at around 40 degrees F for and air conditioner and then absorbs heat into the refrigerant in the evaporator coil. It then returns to the compressor and the cycle is repeated. There are You tube videos that can explain this better than I can. Go to you tube and look up "AC Service tech" and search his videos-1 -
Ok thank upedmec said:charging chart for fixed metering device.0
- 116 Geothermal
- 15.8K Strictly Steam