Wiring timer into indirect water tank
PG13
Member Posts: 2
I have a honeywell aquastat on my indirect . It's wired into it on one of 4 zones on my taco switching relay. How can I wire a timer into this, so I can shut it off during night.
0
Comments
-
You would put the control contacts from the timer in series with the aquastat. You will need a timer where the contacts are isolated from whatever is powering the timer.
Note that a well insulated indirect probably won't cool enough to trigger a dhw call in 8 hours unless it was close to the cut in temp of the aquastat from a hot water draw or you are using some hot water during the night.3 -
You could do this and place a timer on the oil valve or gas valve to see if there is a significant reduction in burner operation over the summer months when there is no call or heat. Maybe 2 months with timer active and 2 months without timer active. I bet you won't see a very big savings as @mattmia2 indicatedEdward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics0
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 129 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 878 Plumbing
- 5.9K Radiant Heating
- 375 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 58 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements