I have a honeywell aquastat on my indirect . It's wired into it on one of 4 zones on my taco switching relay. How can I wire a timer into this, so I can shut it off during night.
0
Comments
-
You would put the control contacts from the timer in series with the aquastat. You will need a timer where the contacts are isolated from whatever is powering the timer.
Note that a well insulated indirect probably won't cool enough to trigger a dhw call in 8 hours unless it was close to the cut in temp of the aquastat from a hot water draw or you are using some hot water during the night.3 -
You could do this and place a timer on the oil valve or gas valve to see if there is a significant reduction in burner operation over the summer months when there is no call or heat. Maybe 2 months with timer active and 2 months without timer active. I bet you won't see a very big savings as @mattmia2 indicatedEdward Young
Retired HVAC Contractor from So. Jersey.
Services first oil burner at age 16
P/T trainer for EH-CC.org0
Categories
- 117.5K All Categories
- 82.8K THE MAIN WALL
- 2.7K A-C, Heat Pumps & Refrigeration
- 43 Biomass
- 402 Carbon Monoxide Awareness
- 8 Chimneys & Flues
- 1.6K Domestic Hot Water
- 4.3K Gas Heating
- 107 Geothermal
- 148 Indoor-Air Quality
- 2.7K Oil Heating
- 45 Pipe Deterioration
- 679 Plumbing
- 4.8K Radiant Heating
- 353 Solar
- 13.3K Strictly Steam
- 2.9K Thermostats and Controls
- 48 Water Quality
- 31 Industry Classes
- 65 Job Opportunities
- 11 Recall Announcements