stack relay disconnected is this a problem?
Joseph_4
Joseph_4 Member Posts: 320
I have a customer with an old coal fired boiler converted to gas using an economite ds24 spark ignition. I got called because no heat (problem was switch in no 369 Lwco) Aside from that the system is archaic..... The fact that the stack relay was bypassed probably years ago....is that a safety issue.. Its been about 10 yrs since i was in class for these, but if the spark module on the economite has its own safeties, then its correct that the Stack relay can be disconnected.. I just would like to make sure. Is that correct?
Thanks
Joe
HHI Services LLC
  • Ironman
    Ironman Member Posts: 7,899
    I’d have to see it to know how it’s set up, but any modern burner should have a built in flame safety.
    A stack switch would be totally worthless on a gas burner due to the amount of time it would take to react to an ignition failure.
    Bob Boan
    mattmia2STEVEusaPA
    mattmia2 Member Posts: 16,394
    Probably left over from a previous oil burner.
    EBEBRATT-Ed Member Posts: 20,063
    Left over from an old oil burner, The Economite isn't using the stack switch.
    HVACNUT Member Posts: 7,393
    Agree it was just never removed after the conversion. Which begs the questions, was a gas barometric relief installed? In the correct location? With a spill switch?