Is this functionally the same as closely-spaced tees?
rsilvers
Member Posts: 182
Does this work for primary / secondary? Is some reason why someone did it like this?
I have only see closely-spaced tees. Will this kind of connection work the same way?
It’s a bit like how a hydro separator is oriented.
It’s just that I see a pump on the boiler side and then a pump for each zone. So that makes me think it is a primary / secondary system.
What you have is some very nice workmanship performed by someone who does not understand primary/secondary and who has a serious pump addiction.
Its probably not so bad that it needs "sawzall therapy". IMO, if you open that valve all the way, you will have workable hydronic separation. I would feel the pipes above the circulators when only one zone is calling to make sure the boiler circ is not "ghosting" the zones that are not calling."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
I kinda' curious as to what wireless thermostats are installed on that system.0
What’s the purpose of the strap on aquastat?Bob Boan
A textbook installation of a separator, nice!Ironman said:A Caleffi Sep4 low loss header looks like it would fit nicely in there and give dirt removal and air separation while accomplishing hydraulic separation.
Living the hydronic dream2 -
Interesting, velly, velly, interesting. You need help by a hydronic specialist.
You can discuss with your hydronic specialist whether closely spaced tees or a hydro sep is in your future.0 -
Maybe that boiler has a second set of S&R for piping an indirect? That may be why the two circs under the boiler?
Primary/ secondary should be explained as aka closely spaced tees or a hydraulic separator devices. I don't see either in that piping?
What you have is a direct piped boiler. Also, your boiler pump is in series with the zone pumps, so doubling the head. But with all those zone pumps I'm not sure what head you see as they rotate on and off.
I suspect with one or two zone pumps calling you have some fairly high flow velocities. Noise?
Perhaps the bypass mitigates some excessive zone flows. Wonder what the adjustment procedure is?
Does the installation manual show that piping option?
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/CHS-110-slantfin-install.pdfBob "hot rod" Rohr
But it also sort of looks like it is a combi and has a dhw recirculation pump.hot_rod said:Maybe that boiler has a second set of S&R for piping an indirect? That may be why the two circs under the boiler?
I suspect the original installer was using those gauges to adjust it, still not sur if they were a genius and it makes sense if you knew what was happening in their head or if they just kept adding stuff on until everything was connected.hot_rod said:
Perhaps the bypass mitigates some excessive zone flows. Wonder what the adjustment procedure is?0 -
Some pics of the boiler close ups of the pump piping and some pics further away of the manifold piping would be helpful.
You don't have a primary/secondary sys. You have a conflict between the boiler pump and the manifold pumps.
With that boiler I would want a separation between the boiler sys and the load sys. Get rid of that crossover. That ball valve is the wrong type of valve, anyway for a bypass. It probably has low valve authority. Under other circumstances a 1/2" globe valve would have been adequate. Just my thinking.0