Best method for finding crack heat exchangers
Dairon421
Member Posts: 49
in Gas Heating
Hey guys what is the best method to find a cracked heat exchanger. I know you can look at it with a camera but it only shows a small percentage of the furnace. I heard of a powder you can use but never tried it. What are your thoughts?
0
Comments
-
-
-
-
The flame may change, the draft may change, when stopping and starting blower motor. You may get Co in ductwork.
With a high efficiency furnace you can seal the end of the flue pipe with saran wrap and watch the saran wrap while someone starts and stops the blower if the saran wrap moves the hx is toast1 -
This is definitely much less of a science than I was led to believe...0
-
EBEBRATT-Ed said:The flame may change, the draft may change, when stopping and starting blower motor. You may get Co in ductwork. With a high efficiency furnace you can seal the end of the flue pipe with saran wrap and watch the saran wrap while someone starts and stops the blower if the saran wrap moves the hx is toastFixer of things
Lead Service Technician
HVAC/R
‘09Moto Guzzi V7
‘72CB350
’83Porsche9440 -
-
Unless I could actually see the crack, I did 4 tests.
1. CO2 with blower on and off. must be at least 2% difference. (because the change in air pressure in the furnace room can actually change the CO2 by 1% even with a good HX.)
2. Draft over fire with blower off and on.
3. Draft at breach with blower off and on
4. Smoke
..a. a smoke bomb in a gas heat exchanger and a smoke tester in the plenum.
..b. Run an oil burner extra rich to produce #10 smoke inside the HX and test the plenum for smoke.
(both a. and b. with blower off)
I always liked at least 2 tests to confirm the crack when not visible. (like #1 and #2 or #3 and #4 or #1 and #4)Edward Young
Retired HVAC Contractor from So. Jersey.
Services first oil burner at age 16
P/T trainer for EH-CC.org1
Categories
- 117.8K All Categories
- 82.9K THE MAIN WALL
- 2.7K A-C, Heat Pumps & Refrigeration
- 44 Biomass
- 406 Carbon Monoxide Awareness
- 11 Chimneys & Flues
- 1.6K Domestic Hot Water
- 4.3K Gas Heating
- 107 Geothermal
- 149 Indoor-Air Quality
- 2.7K Oil Heating
- 45 Pipe Deterioration
- 697 Plumbing
- 4.9K Radiant Heating
- 353 Solar
- 13.3K Strictly Steam
- 2.9K Thermostats and Controls
- 48 Water Quality
- 31 Industry Classes
- 65 Job Opportunities
- 12 Recall Announcements