Hoffman #75 Main Vent

Options
bobbob
bobbob Member Posts: 70
Does not seem to function consistently. Tried the vinegar soak. IS THERE A WAY TO DISASSEMBLE TO CLEAN? Will it do any good, or has it become faulty with age?

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 26,169
    There is no way that I know of to take those apart. At least not so they can be put back together. If it won't open after a vinegar soak and a sharp rap or two, it's done.

    And check your boiler pressure. That vent has a maximum working pressure of 3 psi, and a maximum pressure before damage of 15 psi.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Steamhead
    Steamhead Member Posts: 17,886
    @bobbob , time to replace it. How long is the steam main it serves, and what pipe size?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • bobbob
    bobbob Member Posts: 70
    That vent was in use since we bought house 21 years ago. My 0-5 lb pressure guage reads under 4 ounces
    max. Thanks for the responses. These are pretty cashy. Hoped it could be fixed...
  • JUGHNE
    JUGHNE Member Posts: 11,456
    I think the green paint dates it way back.

    A Gorton 2 will vent twice as much for the same money....they have gotten some bad reviews lately...hopefully the quality control has improved.

    A B&J big mouth will vent 3 times as much as your 75...a little more money and also no float to stop water if that happens.
  • ethicalpaul
    ethicalpaul Member Posts: 7,762
    Yeah I wouldn’t buy a 75 today. For a real bargain, try this one, functionally equivalent to a Gorton #1


    If your pressure stays the same or goes a little lower in the startup phase, then you’re all set

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • bobbob
    bobbob Member Posts: 70
    The problem with this vent was it is not closing--at least, not fully. I tapped on it several times and it closed, but I can't be there to tap every time the boiler cycles. It may have been here long before I became the HO in 2000. I intend to go ahead and replace it as you have advised. Thanks again for you all's inputs!