Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

need to fill 90 gallon whirlpool need help sizing indirect

mikedo
mikedo Member Posts: 174
i have a wbv-04-150 peerless oil boiler i think it is 178000 but output. the tub needs close to 90 gallons for them to use it. they have a 40 gallon super stor now no mixing valve. it fills less than half way. i was thinking of using an htp 80 at 150 degrees and mixing it down to 120. i was going to upgrade the feed and return to 11/4 with a larger pump and put it on priority. the tub faucet runs at 7gpm. i don't know how to do the math to see if it would work. i called htp tech support they said they only know how to fix them and can't help with the sizing. any help would be greatly appreciated. i don't want to put it in and have it not work. that would make it hard to get paid and its going to be quite costly to do the install. thanks mike

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,453
    So you want to draw 7 gpm of 120 degree water 90 gallons of water to fill the tub

    90/7=12.9 min to fill tub


    If you install an 119 gallon tank 80% of the water is considered hot so 119x.8=95 gallons of water.

    stored at 150 you need 5 gpm of 150 degree water mixed with 2 gpm of 50 degree water to get 7gpm of 120 degree water

    so 95 (tank capacity)/5gpm (water needed)=19 min of water draw available, you need 12.9 min.


    If you install an 80 gallon tank @80%=64 gallons available 5gpm @150 needed=64/5=12.8 min available

    So an 80 gallon will give you 12.8 min and you need 12.9 so its about the right size.



    But the boiler will make some hot water after you start drawing

    But your city water could be colder than the 50 degrees I used



    So to be safe you should measure the incoming water temp & then consider increasing the tank size to 119 gallon or increasing the storage temp to say 160


    With no storage to heat 5 gpm from 50-150 (100 degree rise) would take 252,000 BTU/hour


    maybe someone else will have better math than me


    STEVEusaPALarry WeingartenPC7060kcopp
  • Hot_water_fan
    Hot_water_fan Member Posts: 1,823
    @EBEBRATT-Ed I think he meant 120 from the tank, probably less at the tub faucet. If it's 107 at the tub, then you only need 4 GPM of 150 mixed with 50. I think @mikedo could win a lot of favor if he first tries a mixing valve and solves the issue without increasing indirect size.
    rick in Alaska
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,453
    @Hot_water_fan

    I took it that he needed 90 gallons of water to fill the tub at 7gpm flow rate. Indirect stored at 150 mixed to 120 would need 5gpm if the city water is 50 deg 7gpm flow

    I agree the 120 is hot but your going to lose some temp due to piping loss and water cooling during a 12 min fill into a cold tub and not knowing the city water inlet temp. I think he needs an 80 gallon indirect and up the storage temp if need be
    Hot_water_fan
  • hot_rod
    hot_rod Member Posts: 22,022
    At some point the boiler will fire and that 178,000 will be helping cover the draw
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    PC7060
  • Jamie Hall
    Jamie Hall Member Posts: 23,168
    Classic. When filling a tub of that sort (for that matter, even filling an ordinary tub), first, you want hot water. 105 isn't going to do it. Second, you need to hold that temperature. While it is true that the heat from the boiler will be helping, even if all that heat could be transferred to the indirect (it doesn't) you'd still be short. I'm a little conserative -- but not, I think, unduly so -- and I'd want to see the storage tank volume close to the tub volume unless the faucet flow rate is significantly less than the recovery rate.

    So -- minimum 80 gallon indirect.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Zman
    Zman Member Posts: 7,561
    That's a pretty big boiler. If you turn the fill flow rate down a bit it will take longer to fill the tub but you won't run out of hot.
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • hot_rod
    hot_rod Member Posts: 22,022
    90 gallons to the over flow? 15 or so will go down the drain when someone hops in😗
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,453
    The tub flow is high at 7 gpm. But that's what the OP provided. 80 gallon indirect should do it. he can always up the storage temp
    steamedchicago
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 7,720
    edited January 2022
    After reading this discussion, and with the current outdoor temperature, all I can think of is climbing into that tub right now!

    We did a 120 gal whirlpool tub with a buderus boiler connected to a Buderus 40 gallon indirect. Used a mixing valve. Set the tank temp to 160° and it took about 20 minutes to fill the tub. The recovery on the indirect was fast enough to keep the tap temperature at 122° for the 20 minutes. The water was cooling the entire time it was filling so by the time it was full, the tub was at about 116°. Just right for me and my wife. and my girlfriend

    Edit: My wife and my girlfriend are the same person. What were you thinking?
    Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics
    ZmanPC7060
  • mikedo
    mikedo Member Posts: 174
    thanks for the help I'm also considering putting 2 on demand lp heaters in twined together. they are getting a pool boiler so i could tap into that
  • tim smith
    tim smith Member Posts: 2,752
    edited February 2022
    Add a 2nd SSu 50 in parallel store at 150, should be good to go. Gives you 80 gals hot, with recovery could probably get away with 120 unmixed. Whoops, missed it was a 40, still double up and store hotter with mix valve.
    Good luck
    Tim