One Pipe Steam Heat system and replacing the return in the basement
Geoffrey Chambers
Member Posts: 3
Over the years the house has settled and the return in the basement doesn't drain well. There are all kinds of repairs to the pipe because of it and I am considering replacing the whole run in the basement and correct the drainage/flow to the boiler. What would be the best type of pipe to use? My experience is the black pipe didn't hold up well.
I confess I use copper L tubing on wet returns.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes2 -
There is an error in your statement here. Settling cannot harm the return unless it forces some of it above the boiler's water line. A return does not have to pitch toward the boiler. It can be level, or it can even run uphill to the boiler as long as the entire wet return remains below that boiler water line.
Of course, sediment will collect in any low spots so you don't want it to be ridiculous, or if it is a little ridiculous, you at least want some tees and valves available to flush part or all of it.
I made mine with black pipe because it's only about 8 feet long, but if/when that ever fails/rusts out I'm 100% going to replace it with pex. I'm not even kidding.
Finally, it has been my observation that people are very very quick to blame the return for things that are actually caused by poor near-boiler piping. If you care to describe your symptoms, it would be interesting to hear what you're dealing with.
Edit: @JUGHNE has a great response below. My post is assuming wet returnNJ Steam Homeowner.
Is this return line lying on or just above the floor but under the boiler water line as you see it in the sight glass?
Or is it hanging from the ceiling and all above the water line.
If this is the case then the steam main piping may have suffered loss of slope from house settling.
Pictures of the piping system are needed to clarify the problem.1
- 15.8K Strictly Steam
