Radiator vents hiss when system shuts down
bwroga
Member Posts: 44
The steam system in my house seems to work well. All the radiators warm up and only one of them makes a clanking sound.
In "We Got Steam Heat", it says that if you can hear your radiators venting, it is your system crying for help. I don't hear them venting when the system is on, but when the system shuts off, I can hear air getting sucked in through them. Is this "my system crying for help", or is the book referring to an audible hiss when when the system is on and air is coming out of the vents?
Hearing air sucked in at a radiator when the system shuts off isn't really a problem... but it may indicate that the main venting isn't adequate, or is located in such a way that it cools less rapidly, and the air pulled in by the condensing steam has to come from the radiator vents instead.Br. Jamie, osb
I turned the thermostat up a few degrees and went into the basement to look at the main vent. I was hesitant to hold a flame up to the vent, just because it is so close to the ceiling joists. The main vent was silent at first, but towards the end of the heating cycle it was making a loud hissing noise.
Poor little thing. I'm sure it's doing the best it can, but... just isn't big enough. Also, what pressure is it being run at?Br. Jamie, osb
The pressuretrol is set to 0.5 with a 1.0 differential. The pressure gauge says 0, but it's a 0 - 30 psi gauge.
What type of vent would be a good replacement?0 -
Usually mains complain when pressure hits 2-3 psi.0
When you say "at the end of the heating cycle" do you mean after the firing has stopped? Because in that case, there will be a large "inhale" of air into the system that is going to happen somewhere and wherever that "somewhere" is, it will usually be heard.
That's not to say your main vent isn't undersized...that can't be judged by the restoration of air into the system after it's done making steam.NJ Steam Homeowner.
I think the pressuretrol is set as low is it can go (0.5). Am I wrong? Should I lower the differential?0
If it's on a pigtail first check that it isn't clogged0
I use a stick of incense instead. Great for finding drafts too.bwroga said:I was hesitant to hold a flame up to the vent, just because it is so close to the ceiling joists.
Not only is the main vent too small, but the location of the drip it's mounted on is baffling. It should be at the end of the main, but I'm seeing what looks like steam pipes coming from two directions. I'm not sure I can figure out what's going on from the pictures. You might want to get a pro out to your house and have them look over the piping at some point, but for now, get a main vent, like a Gorton #2, and mount it up on a pipe nipple as high as you can so it won't get clobbered by steam hammer.Just another DIYer | King of Prussia, PA
Possibly contributing to your odd venting of radiators;
Your main vent looks to be connected where the end of mains (EOM)
join together.
Steam travel in each main will never be equal. The shorter main will get steam to the EOM before the longer one does.
When that happens the main vent will close.
The longer main will still have air that will probably get vented out the rad vents.
And on shut down the vacuum will create some hissing at rad vents.
Each EOM pipe needs to drop down to the floor separately into the wet return pipe at the boiler. Each EOM needs it's own air vent.
The 2 EOM's must be separated by their own water loop.
This is created when each drop down to the wet pipe.
Your near boiler piping is quite interesting.
Amazing what can work fairly well.1 -
Is this something that is safe to try to do myself?cross_skier said:If it's on a pigtail first check that it isn't clogged
Here is a map of the steam pipes in the basement:
Does the fact that I heard such a loud hissing coming from the main vent indicate that it isn't closing when it should?JUGHNE said:Possibly contributing to your odd venting of radiators;
Is it possible that since the main vent won't close, the pressure can't get high enough to trigger the pressuretrol?