Mystery: Main vent air eliminator keeps breaking
edg2103
Member Posts: 12
I have a one-pipe steam heating system set to 1.5PSI. I bought the house last year, and the system had been leaking from a corroded main. Recently, I had a plumber switch out the rusted pipes. When he turned on the system, we noticed an 3/4"x1/2" air eliminator on a 1-1/2" main was busted (looked cracked). I replaced it with another one with a Home Depot air vent, but that one was stuck on the open position within a couple of days. Replaced it again, with a Gorton #1 air eliminator, but that one only lasted a couple of days as well.
Anyone know what the issue could be? The image of the eliminator and nearby pipes is below.
One thing I noticed is that the nipple seems a little long, online I've seen 6" nipples recommended. Could this cause the vent to be damaged?
Or could it be the vent is not well pitched or poorly located? In the pic above, you can see that the slope from the tee to the elbow is downard instead of upward. Could that be causing water hammer if condensate gets stuck in that elbow? And could that water hammer break the vent?0 -
Thanks Jamie. Are you suggesting the pressuretrol may broken? It clearly indicates ~1.5 PSI on the pressuretrol, see below...
How can I check if it's working properly?
Those pressuretrol scales are notoriously inaccurate. I'd suggest installing a low pressure gauge (0-3psi) in parallel with your 0-30 psi "code" gauge.edg2103 said:Thanks Jamie. Are you suggesting the pressuretrol may broken? It clearly indicates ~1.5 PSI on the pressuretrol, see below...
How can I check if it's working properly?\
There's no issue with a long nipple for a mains vent. Do the failed vents spit water?Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.1 -
@delcrossv, the vent doesn't spit water, just moist steam (which of course, condenses into water). Will look into a low pressure gauge, thanks!1
@edg2103
If it's piped like I think it is it could be part of the problem.
The vent is dead ended at the end of the main.
It looks like that tee is laying on it's side looks like it's tied into that 1 1/4" copper drip that comes off the side of that tee.
That means that main is 1/4 full of water1