Pumping away from the Compression Tank, on a Primary-Secondary heat system
bloombrewing
Member Posts: 5
Most all the pictures I see of a Primary-Secondary system, with close-spaced tees, always seem to show pumping towards the expansion tank, not away. Dan Holohan has a book on "Pumping Away" but all I see is towards.
I can't speak for anyone else, but I would have connected the x-tank to the bottom of the air eliminator.
Also, are those swing check valves on the suction side of the pumps? On the vertical?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
This is a picture from www.radiantcompany.com, not my job
It does appear that they are single-swing checks before the pumps on the vertical
I agree with putting the tank on the bottom of the air separator, but I often see similar setups like this picture, and wonder????0 -
@bloombrewing you should always pump away from the expansion tank if at all possible. With primary secondary the expansion tank should be on the common piping not the boiler loop1
It's worth remembering that not all photos are the best way to do things. Also that there are a number of ways to do things which work -- just some work better than others.Br. Jamie, osb
Is that a tankless water heater? Usually with high pressure drop appliances you want to pump into it
judging by the Y strainer you are pumping out of the heater?Bob "hot rod" Rohr
Why so many drains? The Pumping Away schematic only has one at the boiler outlet.0
Yes, there seems to be unneeded drains, or purge ports. The 2 at the heater would be to service the heat exchanger when cleaning. The 1 on the "drop" at the Return manifold would be to purge the two zones of any air. The 2 that are before and after the air-seperater and the one near the pumps, I have no idea why they are there and really not needed. Not my set-up, just a picture taken from a Heating supply web site.0
- 121 Chimneys & Flues
- 15.8K Strictly Steam