Pumping away from the Compression Tank, on a Primary-Secondary heat system
bloombrewing
Member Posts: 5
Most all the pictures I see of a Primary-Secondary system, with close-spaced tees, always seem to show pumping towards the expansion tank, not away. Dan Holohan has a book on "Pumping Away" but all I see is towards.
0
Comments
-
I can't speak for anyone else, but I would have connected the x-tank to the bottom of the air eliminator.
Also, are those swing check valves on the suction side of the pumps? On the vertical?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
This is a picture from www.radiantcompany.com, not my job
It does appear that they are single-swing checks before the pumps on the vertical
I agree with putting the tank on the bottom of the air separator, but I often see similar setups like this picture, and wonder????0 -
@bloombrewing you should always pump away from the expansion tank if at all possible. With primary secondary the expansion tank should be on the common piping not the boiler loop1
-
It's worth remembering that not all photos are the best way to do things. Also that there are a number of ways to do things which work -- just some work better than others.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Is that a tankless water heater? Usually with high pressure drop appliances you want to pump into it
judging by the Y strainer you are pumping out of the heater?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Why so many drains? The Pumping Away schematic only has one at the boiler outlet.0
-
Yes, there seems to be unneeded drains, or purge ports. The 2 at the heater would be to service the heat exchanger when cleaning. The 1 on the "drop" at the Return manifold would be to purge the two zones of any air. The 2 that are before and after the air-seperater and the one near the pumps, I have no idea why they are there and really not needed. Not my set-up, just a picture taken from a Heating supply web site.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements