Faux 2 pipe on a Baseray.
Seems someone got around the " Don't hook a Baseray up to 1 pipe steam" rule. Interestingly, it works- gets hot no gurgle or bang.
What are all the rust stains?All Steamed Up, Inc.
Consulting0 -
Whole building is like that.(???) Replaced a dozen blown vents. Maybe sometime in the past someone screwed with the pressuretrol? That's my guess. Nothing seems to be leaking out of it now..Steamhead said:What are all the rust stains?
What's connected to the far end of the bottom tube, or is it just plumbed such that only the top tube heats?0
That makes some sense. It seems the idea is steam goes up past the valve through the top tube and condensate returns through the bottom tube to the reducing tee. There's an internal connection between the top and bottom tube, yes?JUGHNE said:This was shown either on the wall or in books.
There was a check valve in the return line, probably under the cover.
The check kept the steam only in the top pipe across the convector and apparently enough build up of condensate water would open the check to drain.
I didn't see a check, but maybe the attempt is by using a smaller tube on the bottom "return".Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
i don't believe so, why i was asking about what was going on at the other enddelcrossv said:
I would say the other end of the convector tube has a tee with the vent on top of it's run and the smaller pipe is connected to the bottom run of the tee.
Then the check valve and connection to the steam riser for drip.0 -
I didn't look closely, but I did not see see any external connection between the top tube and the bottom. Just a vent in the top and a plug in the bottom. (insert confused smiley here). If it's connected internally the rig makes sense.mattmia2 said:
i don't believe so, why i was asking about what was going on at the other endTrying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
I remember the drawlings, the basic idea was to let the baseboard itself operate as if it were connected to a two pipe system. IF there's a top to bottom connection on the far end of these, it's pretty close to what (I think I remember) the drawlings said to do. If not, then only the top section is working, since there's no way for the air to leave the lower section. The rusty marks make me think of leaks. Perhaps that's how they were being vented.0
There’s no end caps on that Baseray, just the cast iron radiator. Therefore, there’s no check valve. The sections of the casting are hollow inside from top to bottom, not segregated. There are tappings, top and bottom, on each end of each 2’ section, either threaded or push nipple.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.2 -
Now it makes sense. In through the top to the vent, condensate out the bottom through the smaller pipe. In any event, the rig works. There'd be a differential in "drag" between the larger top pipe and the smaller bottom pipe (made even smaller with condensate flow).Ironman said:There’s no end caps on that Baseray, just the cast iron radiator. Therefore, there’s no check valve. The sections of the casting are hollow inside from top to bottom, not segregated. There are tappings, top and bottom, on each end of each 2’ section, either threaded or push nipple.
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-242 -
Just watched (for the second time) a Gordo Utube about dead men secrets that showed a 1 pipe convector with the check valve return. Always good Utubes.
I wonder if that small union could have an orifice in it to restrict steam from going that way. Letting the water dribble back down.
(not a dead man theory...not yet anyway
) 1 -
Go to Gordo's channel, plenty of things to watch.
Someone here can do that link....just not me...too challenged. :'(0 -
Thanks Erin!Erin Holohan Haskell said:
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.1
- 50 Industry Classes
