Mixing valve with ODR
ultimatedesi
Member Posts: 7
Hello,
I am facing issues procuring TACO iSeries 1" mixing valve with ODR (I100T3R-1) in NJ 07836. Seems all the suppliers I have tried are showing the valve on backorder. I would like to request suggestions on: 1) If there is any way to procure this item at a reasonable price (a vendor in Canada was willing to ship at nearly double the price!) and more importantly 2) what are other equivalent alternatives that should be considered please.
Appreciate your help. Thanks.
I’m from jersey , may I ask where from , Try to give me email if you can0
This store shows one in stock
404 WEINSTEIN SUPPLY EGG HARBOR
3187 FIRE RD
EGG HARBOR TOWNSHIP, NJ 08234-9601
609-677-0666
OOPS It might be a 3/4"Edward Young Retired
Thanks, Snowmelt and EdTheHeaterMan for your quick response. I have reached out to the store through their website and would see if they have the 1" version. Meanwhile, am open to suggestions on alternates as well. Thanks.0
Are you sure you need a 1”, looks like the cv is higher on some 3/4, other versions are very close Cv.
How many gpm are you flowing?Bob "hot rod" Rohr
Living the hydronic dream1 -
Better screen shot, Cv and weightBob "hot rod" Rohr
This valve will feed 2 zones (total 14 ports with around 270'-280' long 1/2" dia.tubing).Thank you,
Hiren Patel0 -
A smaller valve than the piping it is connected to is actually desirable . You want to use the valve which has a CV rating close to your flow rates . These smaller valve will reach target faster because less water flows through them .ultimatedesi said:Thanks, Snowmelt and EdTheHeaterMan for your quick response. I have reached out to the store through their website and would see if they have the 1" version. Meanwhile, am open to suggestions on alternates as well. Thanks.
732-751-1560
Rich McGrath 732-581-38330 -
You could install one of these as a fixed position mixing valve which should give you an outdoor reset curve that is parallel to the boiler curve. If you decide you want individual outdoor reset, you could add a powerhead and controller.
https://www.supplyhouse.com/Tekmar-710-3-4-Brass-3-Way-Mixing-Valve-4864000-p?gclid=Cj0KCQiAtJeNBhCVARIsANJUJ2EUoN-lgzq8PhHbUyt0l0ejCeZC2gKvh8BFk5szd9cFupspnBxJStkaAsyuEALw_wcB
@hot_rod and @Rich_49 do you think the temp will be stable as the flow changes with one vs two circs running?
Albert Einstein0 -
Here is the pressure drop with 14 loops at .5 gpm each? (7 gpm) use the 3rd box to see the pressure drop at 5.6' head, acceptable.
But I only see 8 loops on the mix valve? if so 4 gpm, which is fine for a 4.5 cv valve.Bob "hot rod" Rohr
There are reducing couplings . The smaller valves are more accurate . SupplyHouse. com can get you the 4 way ODR 3/4" between December 9 - 16ultimatedesi said:
https://www.supplyhouse.com/sh/control/search/~SEARCH_STRING=Taco I Series
The smaller the valve you use will be more stable when circs turn on and off . That's kinda why we mentioned using the smallest valve . You should call me to have a look , I may have the valve body for a 3/4 or 1 " around the shop . You'll probably be able to get sensor and actuator . Call me , I'm in Toms River and may actually be able to get you one , a customer of ours has spare everything in multiples at his house , maybe he would part with one now if it's replaced .
732-751-1560
