Crown royal with steam heat

Options
Imissu72
Imissu72 Member Posts: 1
edited November 2021 in Gas Heating
I have a crown royal heater that was installed 3yrs ago and when I turned the heat on the beginning of November it worked for 2 weeks ... One day I went into basement and it was water pouring out of the front of it.. I  had someone come look at if an he said I need a whole new heater... Is there anything I can do to avoid spending another $? ... I was told this one should last 10 to 15 years..

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 7,833
    edited November 2021
    Options
    Sorry but if your boiler is leaking water, it is shot. It needs to be replaced.

    You might want to get yourself one of these Crown Royals

    What is the serial number? There may be some warranty left on that boiler. It may save you on the actual boiler... Not the Labor which is the lions share of a new boiler price.


    The near boiler piping is incorrect, which may have been a contributing factor in the reason your boiler failed.
    Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics
  • mattmia2
    mattmia2 Member Posts: 9,637
    edited November 2021
    Options
    Did whoever looked at it pull the jacket to see where it is leaking from? It is possible that it is a leak at a fitting or plug or between sections and can be repaired. What is the heat exchanger warranty?

    Please edit to remove pricing.

    If it is installed and applied properly you should get 20-40 or more years.
    Erin Holohan Haskellrick in Alaska
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 7,833
    Options
    Crown Boiler (now Velocity Boiler Works) of Philadelphia is one of the only boiler manufacturers that publish and sell a "Boiler Piping Kit" for the steam boilers they sell. You should get in touch with the installing company and sue their **** for improperly installing that boiler.



    All the guesswork in selecting the proper pipe nipples and fittings are gone when you purchase this kit and follow the instructions. Your copper return piping does not have the required "Hartford Loop" that will insure that steam pressure in the boiler will not force all the water out of the boiler into the return piping resulting in a "Dry Fire" situation that will cause a catastrophic boiler failure.
    Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,519
    Options
    @Imissu72

    What a complete shame! Who ever installed that did not read or follow the boiler installation manual.

    Take the model & serial # and I would call Crown directly and ask about the warranty.

    And whatever you do don't let the original installer back in the house.

    Download the boiler manual and look at the piping diagram yourself. They should not have used copper tubing and it's done all wrong
    Ironman
  • KC_Jones
    KC_Jones Member Posts: 5,737
    Options
    Boiler boiler should last 25 at minimum IMHO.

    What does the digital display on the device I circled read, and have you ever reset it?

    That heat exchanger should still be under warranty I would think, but review your paperwork and find out for sure.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Ironman
    Ironman Member Posts: 7,376
    Options
    The sad thing is that the manufacturer doesn’t have to warranty anything if it’s not piped and installed correctly. Obviously, yours is not and that is the fault of the installer.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    mattmia2rick in Alaska
  • Ironman
    Ironman Member Posts: 7,376
    Options
    Beyond the incorrect piping, there’s likely another issue that caused the failure: it’s likely that you have a leak somewhere - maybe a wet return - that’s caused an excessive amount of fresh water to be added. That can cause an extremely premature failure.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    mattmia2
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,519
    Options
    @Ironman

    If I was the MFG I wouldn't honor the warranty but for the homeowners sake I hope they do and he can find a decent installer. What a mess.
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 9,637
    Options

    @Ironman

    If I was the MFG I wouldn't honor the warranty but for the homeowners sake I hope they do and he can find a decent installer. What a mess.

    it definitely isn't right, but depending on what is going on up higher near the ceiling it may not be as bad as it looks in that picture.
  • Steamhead
    Steamhead Member Posts: 16,832
    Options
    Sure that's a Crown "Royal"? Looks like a Jamaica to me, which is a rebranded Dunkirk. As usual, someone reduced the size of the steam outlet from 2-1/2" to 2", which is another major no-no on this job.

    The current Crown Bermuda series uses 2" top outlets.

    What is the model number of this boiler?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • mattmia2
    mattmia2 Member Posts: 9,637
    Options
    How can you even tell? The riser comes up behind the vent ant you can barely see it then ties in somehow near the ceiling.
  • JakeCK
    JakeCK Member Posts: 1,356
    Options
    Sorry but if your boiler is leaking water, it is shot. It needs to be replaced. You might want to get yourself one of these Crown Royals What is the serial number? There may be some warranty left on that boiler. It may save you on the actual boiler... Not the Labor which is the lions share of a new boiler price. The near boiler piping is incorrect, which may have been a contributing factor in the reason your boiler failed.
    I seriously thought this was going to be someone having a drink after installing a new boiler when I read the title. :s

    But I guess they we're having a drink over the death of their current one.