smell from steam radiators
homeownersteam
Member Posts: 3
I had new Weil Mclain steam boiler installed a month go, i flushed 3 times and skimmed it 4 times and still get a strong smell from radiator vents, smell is in boiler when skim cap plug removed, plumber used existing pipe. Old weil mclain i had for 35 years with no smell , i am wondering if the cast iron making process was changed
No, cast iron is still cast iron. And it's still loaded with oils when it's cast. Flushing won't help at all. Skimming, however, will -- but may take hours and hours.Br. Jamie, osb
Find out how much water you boiler holds to the normal water level. Put in 1 pound of TSP/50 gallons of boiler water.
So if the boiler holds 10 gallons of water you put 16 ounces/50=.32ounces/gallon
.32 x 10=3.2 ounces for this example.
Mix the tsp in a pail and pour it in through the safety valve tapping or skim tapping with an elbow turned up.
Run the boiler until hot and shut it off when the header starts to steam. Leave the burner off
Skim very slow, the stream should be the size of a pencil or less. Add water as needed.
You may need to skim several hours
When finished drain boiler, let it cool refill and drain, refill and drain again then refill and bring to a boil0 -
thanks for input0
- 117 Geothermal
