Running control cable with Liquid Refrigerant Line
SENWiEco
Member Posts: 164
Good Day folks,
Search for this but did not find any hits. Would there be any reason I could not run my 18ga control cable through the same foundation penetration as the insulated heat pump liquid refrigerant line?
The house is a high performance dwelling and all penetrations are air sealed on outside. The foundation is insulated on outside surface.
I did not allow for enough penetrations, so I would have to dig out gravel, strip dimple membrane and insulation off and then drill and seal the new penetration if I can not run cable with liquid line (cant use suction line hole as just big enough for insulated pipe).
FYI, the line-sets immediately exit below grade (and are well insulated against foundation where below grade - aprox 12") and will be run against wall not buried in case someone was going to yell at me for burying it :-)
Many Thanks for your insight
Sean Wiens
Not the greatest. I mean what kind of cable can you run underground that is suitable for direct burial?
I would prefer to see a whip of non metallic seal tight run from the condensing unit to the interior of the house.
I know it's standard practice to run regular thermostat wire from the condensing unit to the house exposed outside and it's done all the time but
That stat cable I am sure is not listed for burial, outdoors exposed and has no UV protection1 -
Thanks @Ironman - yes will protect. Was worried there would be a temperature reason not to do this. Sounds like I am good
@EBEBRATT-Ed - I will be running the line sets through a PVC cover channel and would run the 18ga HVAC cable along with the liquid line (strapped to outside of insulation). Other than exit from foundation, this cover/channel would all be above grade mounted to wall. The part below grade is only 6" and the surrounding fill around the PVC cover/channel is very well drained gravel.Sean Wiens0 -
How much line set runs underground?0
Thanks @JUGHNE I am planning on similar. I have the gravel covered, that side of the house is backfilled with gravel so all the way from grade down to the footings 12ft below. I plan on a 10" piece of PVC cut in half to create the access 'well' once the concrete sidewalk is poured in area.Sean Wiens0
IMO, half of a 10" pipe seems small.
Consider having to change the large suction line, it would require a brazed 90 fitting where it exits the wall below grade. Perhaps there is one there now.
I am thinking of 1/2 of perhaps a 16" round galv metal culvert. This would be scraps to a street dept.
In any event I think you would want this to extend up a couple inches above the sidewalk.
You would want a finished edge at the top.
There are also some 1/2 circles of fiberglass that are used in septic drain fields. IDK the correct name of them. Someone here may know what I mean.1