Wiring thermostat to boiler
stratsg
Member Posts: 5
Oil fired boiler
2 zones
2 zones
2 thermostats but one is not wired to boiler. Looking for correct way to wire the 2nd thermostat.
In pic there is a red/white wire from zone valves to transformer (?) and red/white wire of first thermostat with reds connected to each other and whites to trans former.
Also a single red wire running from zone valve to transformer.
In picture you can also see the unwired second thermostat wire.
My question would be where to attach the red and white wires of the second thermostat?
Also feel free to correct any of my incorrect terminology. Carpentry is more my thing.0
Guess I'll have to find my glasses so I can actually read that. Thanks0
Any chance I can get more of a "put the white wire here/ put the red wire there" answer? I'm trying to get heat to my mom's bedroom for the night.
You can always just manually open the zone valve to get the heat to flow to the problem zone.
Here is the wiring diagram from the valve manufacturer,
As @Jamie Hall said, electric is colorblind but this diagram has some a helpful hints where the R terminal from the transformer MUST go to the R terminal of the thermostat.
The W terminal for the thermostat MUST go to the 1 terminal of the zone valve.
The C terminal of the transformer must go the the 2 terminal of the zone valve
Finally the #3 and the #2 terminal will operate the boiler control
Important to be sure to wire all the zones the same. if you mix up the thermostat or transformer wires from one valve to another, you could burn out the transformer on the boiler control. I have had many professionals come to me with incorrect wiring of zone valves that cause the transformer to fail. And the transformer that fails is never the easy one to replace. It is always the transformer on the expensive boiler control that fails. and that one is not replaceable. You need to purchase the entire new expensive boiler control.
EDIT: From the out of focus photo it appear that the wiring is not exactly as the manufacturer diagram indicates. I have seen where another wiring design will work, but when there is a problem (like you are experiencing) it becomes difficult to determine where the problem is. Also it appears that the #2 and #3 terminals ARE connected to each other via a jumper wire and therefore both are connected to the boiler control. Perhaps you have a defective valve actuator. This is common and one of the reason there is a manual lever on the valve to offer a way to heat the zone until a replacement part can be purchased.
Mr.EdEdward Young Retired
Those 3 wire Taco zone valves are a little complicated to wire. I would suggest upgrading to a zone controller and wiring it per the instructions. https://www.supplyhouse.com/Taco-ZVC403-4-3-Zone-Valve-Control-Module-with-Priority"If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
Not really... I did find them confusing at first, but once you get used to the idea that that middle contact is used for two different circuits it's not too bad... if slightly wacky.Zman said:Those 3 wire Taco zone valves are a little complicated to wire. I would suggest upgrading to a zone controller and wiring it per the instructions. https://www.supplyhouse.com/Taco-ZVC403-4-3-Zone-Valve-Control-Module-with-Priority
- 87.1K THE MAIN WALL