240V heater and low voltage thermostat
        
            Options        
            
        
                
                    AmateurHour                
                
                    Member Posts: 2                
            
                        
            
                    Looking for a little confirmation from the experts on this. I have a 5000W DynaGlo heater in my garage and I'm setting it up for external thermostat control. It has a switch and terminal block for external control with a line voltage stat. I'm using an Aube RC840T-240 transformer/relay and an ecobee 3 lite stat. I've attached a sketch of what I think is how this should be wired in order to retain functionality of the internal thermostat as I believe it controls the fan delay start and cool down run.
Thoughts? 
                
                Thoughts?
 
                0                
            Comments
- 
            Refer to the wiring diagram which is helpfully printed on the case of the RC840T-240 and the heater's diagram. You can have either the heater's thermostat active or the external one -- but not both.Br. Jamie, osb
 Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
- 
            
- 
            How does this look? 0 0
- 
            
- 
            @AmateurHour : I am doing exactly the same thing as you with a 5000W DynaGlo heater and an Aube RC840T-240 transformer/relay, but with a different thermostat.
 Did your corrected wiring diagram work out successfully?
 Thank you.0
- 
            I tried both ways and it did not work for me.0
- 
            Did you wire it in accordance with the Aube wiring diagram?
 https://www.manualslib.com/manual/11515/Aube-Technologies-Rc840t.html
 Note that you have a choice: external thermostat or internal thermostat. NOT BOTH.Br. Jamie, osb
 Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
- 
            I might add -- you will need a two pole service disconnect for that heater, as the Aube relay only breaks one of the hots, not the other.Br. Jamie, osb
 Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 111 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements