Lost system pressure, boiler shut down.

Jimbo_5
Jimbo_5 Member Posts: 218
Just experienced an unusual boiler shut down. Woke up to no hot water in the shower. When down to the basement and found the boiler (Triangle Tube Prestige 110) trying to fire. Looking around I noticed the gauge on the supply line was at 0 psi, rather than its usual 14 psi.

After looking around finding no obvious water leaks or signs of leakage, I opened the closed makeup water valve. You know how slowly they fill, yet in seconds the gauge was back at 14 psi. I closed the valve again and fired up the boiler. It has been running fine ever since. The boiler was installed 12 years ago, has 2" supply and return black iron pipes from an old gravity system circling the basement feeding 9 cast iron radiators and 2 rooms of ci baseboard on 2 floors. It also heats a Triangle Tube indirect 30-gal hot water tank. This problem has never happened before. Two years ago the expansion tank failed for reasons unknown. Replaced it and all was fine.

I cannot figure out what might have caused this to happen. Any ideas? Perhaps the Spirovent eliminated some trapped air? Thanks in advance for any help.

Comments

  • mattmia2
    mattmia2 Member Posts: 9,572
    How often did you check the pressure? It could lose enough water to get to 0 psig through minor seepage at valve packings and such over months or years. If it only needed to replace essentially the water beginning to compress the diaphragm in the expansion tank then it wouldn't take much to replace that water. You should check it when the whole system is at temp to make sure it doesn't go up too much and the expansion tank is doing its job and you should check it again cold if the boiler was hot when you filled it because it will go down when the boiler cools if you have the auto feed closed.
    Solid_Fuel_ManZman
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,452
    @Jimbo_5

    If you only added a little water and the gauge jumped up quickly it is probably an expansion tank issue
    delta TZman
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    How long since the air pressure in the expansion tank was checked? You need to bleed to system to 0 psi and set the air pressure to 12 psi if you are running a 14 psi system. You likely have two ex60 tr anks if it was a gravity system. Very large volume of water comparatively speaking. 
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • psb75
    psb75 Member Posts: 828
    It also could have been just an air-lock situation. Interesting that you operate the system with autofeed valve shut off. Maybe leave it open? I daresay most ARE operated with valve left open. You CAN operate it with the valve closed, but either YOU or a device has to monitor the fill-status/pressure of the system then.
  • Ironman
    Ironman Member Posts: 7,367
    In an old system like that there can be some very small leaks, usually the packings on radiator valves, that are almost unnoticeable.

    There was a long discussion on here a few years ago about leaving the fill line open or closed. I think the best advice was to leave it slightly cracked open to maintain pressure on the system. That way, if there was a catastrophic leak, the fill line would only provide a small steam of water instead of full blast.

    A Caleffi fill valve has a knob where you can throttle the flow down once the system is filled.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 9,572
    Ironman said:


    A Caleffi fill valve has a knob where you can throttle the flow down once the system is filled.

    Oh, is that how that is supposed to work? I wasn't clear from the instructions that the knob could be used to throttle the flow.