Newly roughed in radiators not warming up

NG fired steam boiler converted to water

2 sets 2” copper supplies and returns for risers then horizontal mains are 2” black iron 

No circulator or zones, 1 thermostat 1st floor(basement, 1st, 2nd, office in attic)

customer wanted to install new bottom piped rad on 2f addition and relocate previously installed bottom piped rad on 2f addition(back to back rooms)

one rad on 2f gets warm, hot at supply valve, but only warm rad. Newly installed rad remains cold. All lines were pressure tested and rads have been pressure tested

need help here boys! All other rads including attic get hot hot hot. Addition rads not working properly 

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,170
    I hope there are bleeders at the top of the new radiators, and that they have been thoroughly purged.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Might be an air problem. Have all the radiators been bled and all the pipes been purged of air?
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • Ironman
    Ironman Member Posts: 7,367
    “No circulator or zones, 1 thermostat 1st floor(basement, 1st, 2nd, office in attic)” 

    Are you trying to achieve flow by gravity?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    PlumbBob2075
  • PlumbBob2075
    PlumbBob2075 Member Posts: 8
    They all have bleeders and were purged of air, supply and return fittings all new from supply house, is acting as a gravity fed system. My 2 problem children both have 3/4 lines(S&R) for each, piped in 3/4 HePex, but are tied together respectively to a branch off the 2” black iron main. 
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,455
    @PlumbBob2075

    Confused. If you converted a steam system to gravity hot water and don't have a circulator that's an issue

    If your trying to heat radiators with 3/4" pipe on gravity that probably won't work without a pump
    kcoppIronmanRich_49EdTheHeaterMan
  • PlumbBob2075
    PlumbBob2075 Member Posts: 8

  • PlumbBob2075
    PlumbBob2075 Member Posts: 8
    @PlumbBob2075 Confused. If you converted a steam system to gravity hot water and don't have a circulator that's an issue If your trying to heat radiators with 3/4" pipe on gravity that probably won't work without a pump
    We did not convert, unit has been converted by an outside contractor. I’m green when it comes to gravity fed systems. I’m in the process of reading Dan Holohan’s Classic Hydronics. Helping, but need answers sooner 
    Kybeans403
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,455
    @PlumbBob2075

    I fear the pex will not be large enough to heat the rads without converting to forced hot water with a pump.

    Also, the unavoidable ups and downs of the pex loops will make air removal very difficult when operating gravity


    I think (and I am making some assumptions) if the "original house" was and remains gravity and worked in the past then make the new rads on the pex system a different zone with a pump.

    What I would be concerned with is the pump flow disrupting the "original" gravity flow. This could be solved with a small brazed plate heat exchanger.

    I doubt your going to have any luck making the pex system work on gravity

    We will see what others that know more than i have to say
    mattmia2
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 1,954
    Never going to work without a circulator. You will probably need to separate into different zones. Zones with the smaller pex will need to be separated from zones with larger pipes. You will have flow issues otherwise. Proper piping by the boiler might be helpful. Separation of some sort is the key.
  • Ironman
    Ironman Member Posts: 7,367
    Not only do you need a circulator(s), but I don’t see an expansion tank. Is there one?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • There's a plain steel x-tank shown in a couple of the pictures.

    @EBEBRATT-Ed said:
    I think (and I am making some assumptions) if the "original house" was and remains gravity and worked in the past then make the new rads on the pex system a different zone with a pump.
    I agree.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    mattmia2
  • JUGHNE
    JUGHNE Member Posts: 11,042
    The gravity systems I have encountered have large horizontal piping, one has 2 x 4" main take offs of the boiler. The returns were 2 x 3" dropping to the bottom of the boiler. Supply sloped up away from the boiler and return sloped the same....as if they were drain lines that emptied into the boiler.

    The first floor rads were fed with 1" to 1 1/4" run outs.
    All take offs (first & second floor) came of the top of the main or at a 45.

    Now the second floor rads had only 3/4" risers, they were exposed on the first floor so are easy to follow. One set of 3/4" risers even feeds 2 rads back to back.
    All of these work very well.

    The main feature is that the 3/4" riser goes straight up for maybe 10'.
    I believe the smaller pipe works well because of the vertical rise which induces gravity flow. In the basement the 3/4" may be connected to a 1" horizontal run out off the main.

    If your pex had the vertical rise of the full first floor then you may get the flow needed. The horizontal with some wavy runs may not be friendly to gravity floor.
    Maybe you could you try a solid pipe over sized horizonal run out in the basement, if you had a somewhat straight up shot to the rad. Just a WAG.

    Did you check for restrictive orifices in the supply valves?

  • Steamhead
    Steamhead Member Posts: 16,796
    I agree- that PEX will never work.

    Unless you're willing to convert the entire system to forced circulation, you need to repipe these rads in copper, using the same size pipe as similar-sized radiators in that system.