wood boiler tweaking with underfloor heating
Avice
Avice Member Posts: 7
Hello, i want to tweak this:
Maybe possible run it with only one pump?
Now both pump work on lowest level (5 wats consume).
With this schema boiler temp always ~70*C ~ 75*C
Any ideas?
Thanks for any advice ;)
  • Paul Pollets
    Paul Pollets Member Posts: 3,656
    John Siegenthaler has written extensively on proper piping and setup when using wood boilers or pellet boilers. I suggest you spend some time reading them and get familiar with how to do it correctly, so there's no fire or explosion hazzards.
  • Avice
    thanks.
    now i have questions about one thing
    Do i need a non-return valve in this place? i mark it with arrow? or it's not good idea to place it here?
  • leonz
    leonz Member Posts: 1,126
    you do not require a check valve.
  • GroundUp
    GroundUp Member Posts: 1,907
    No check valve, but a 3 way thermostatic mixing valve will never work properly unless there is a circ pump pulling from the mixed port. If the one in your diagram is thermostatic, that is.
  • Avice
    edited September 2021
    both mixing valves are thermostatic. i want run it with only one pump if it possible.
    Now it work like this: (yellow color is how water flow.)
    But i want like this:
    It will works if i install check valve in place where i marked `Here` with arrow.?
  • GroundUp
    No, and no. You can do it with one pump, one mixing valve, and zero check valves unless boiler protection is an issue which is likely. In which case, you either need a 4 way valve or 2 pumps and a primary/secondary piping arrangement. If boiler protection is not an issue, the one pump needs to go between the mixed port of the mixing valve and the radiant, pushing toward the radiant and pulling from the valve.
  • Avice
    Thanks.
    so me schema (first image) is good and don't need any changes?
    for boiler protection im using this valve (https://www.regulus.eu/en/dbv1-thermal-relief-valve-insulated).
  • Zman
    Zman Member Posts: 7,569
    You need to have a circulator inside the mixed temp loop. If you do not, the flow rate in the loop varies and you do not get even distribution.
    Albert Einstein
    STEVEusaPA
  • GroundUp
    No, the first drawing will not work as we already told you
  • Avice
    im confused :D
    u mean this drawing?
    (avoid condensation mode)
    here are 2 pumps one for floor and other for small circle.
    Now reading some articles and found scheme like this: (diverting mode)
    which one is better?
  • Zman
    Why not use a taco iseries mixing valve with outdoor reset and condensation protection on the radiant side and lose the other mixing valve and circ?
    The iseries valve will throttle back when the boiler return temp drops.
    Albert Einstein
  • Zman
    That is assuming the owb has no minimum flow requirements.
    Albert Einstein
  • Zman
    If you need both loops to satisfy minimum boiler flows, the loops should be piped primary/secondary so that one loop will not interfere with the other
    Albert Einstein
  • Zman
    Is your wood boiler pressurized? If not, what is it's elevation in relation to the floor it is heating?
    Albert Einstein
  • Avice
    about 2 meters, anyway system under pressure always ~1 Bar.
    i just read this article https://www.pmmag.com/articles/88035-the-do-s-and-don-ts-of-three-way-thermostatic-valves-br-john-siegenthaler-pe
    if it applicable and for wood boiler
    with this loops not interfere with each other. if I understood correctly.
    http://prntscr.com/1szbji5
  • Zman
    You getting the idea. This solution is much simpler and accomplishes the same thing. You also get outdoor reset which, IMO is mandatory in a radiant heat system.
    Albert Einstein
    IronmanAvice
  • Avice
    Zman, thanks for help. :)