Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

In ground oil line abandonment

Options
We removed our oil fired boiler and hydronic setup and are looking to eliminate the remaining components including the burner. Any recommendations on how to handle the oil feed and return lines? How do I cap them temporarily and/or permenantly?

Thanks

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,284
    Options
    Blow them out and make sure there is no residual oil in them at all, and then cap them at both ends.

    What are you doing with the tank?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,506
    Options
    Take the check valve off before blowing it back.
    steve
  • Jamie Hall
    Jamie Hall Member Posts: 23,284
    Options
    The assumptions I make, @STEVEusaPA ... sigh... I assumed they would disconnect right back the elbows... oh well.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,523
    Options
    Yes, what are you doing with the tank?
  • dbldangertilt
    dbldangertilt Member Posts: 3
    Options
    Haven't decided on what to do with the inground 675 tank. Soil samples came back negative. Has about 170 gals left. Would prefer removal vs abandonment (slurry fill).

    What caps are typically used for the lines? Trying to diy as much as possible. 


  • Jamie Hall
    Jamie Hall Member Posts: 23,284
    Options
    I'd agree that removal of the tank is the best approach. Remove it, take soil samples of the sides of the pit, continue soil removal until the samples are all negative. I'd use threaded caps on the lines.

    However... this is not really a diy job. That tank, even after you get it pumped out, is going to be heavy. Further, it's structural integrity is going to be questionable. There are companies that do this for a living and know what they are doing -- and, perhaps more important, carry insurance against problems during removal and down the line if contamination is suspected. Try contacting your public health people or environmental protection people for suggestions.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    STEVEusaPA
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,506
    Options

    ...What caps are typically used for the lines? Trying to diy as much as possible. 


    Whatever you do, unless you break out the concrete you're going to have 2 pipe stubs.
    After you blow out the lines, you can unscrew both elbows and just put on some regular steel caps. Hard to tell by looking buy I think they are 1/2" or maybe 3/4". Is it steel pipe back to the tank?

    If you get the tank dug out, they can probably get the supply/return removed all the way back to the house. If that's the case I'd just fill them with cement at the wall, then cut the concrete floor around them and get those lines cut below the floor and patched.
    steve
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,523
    Options
    @dbldangertilt

    If one or both of those oil lines extend to the bottom of the tank and where you disconnect the lines is lower than the oil level in the tank you will likely get oil syphon to you when you disconnect the lines.

    You will have to cut the lines at the high point or work fast
  • dbldangertilt
    dbldangertilt Member Posts: 3
    Options

    However... this is not really a diy job. That tank, even after you get it pumped out, is going to be heavy. Further, it's structural integrity is going to be questionable.

    Thanks. Yes I was going to contract out for tank removal but try to cap the lines in the meantime.



    If one or both of those oil lines extend to the bottom of the tank and where you disconnect the lines is lower than the oil level in the tank you will likely get oil syphon to you when you disconnect the lines.

    You will have to cut the lines at the high point or work fast

    This is exactly what I think will happen having disconnected lines for repair/maintenance before. A heating oil company will extract the remaining oil for $350 less 50 cents per usable gallon likely leaving 3-5 inches of sludge. I assume we may still get oil in the lines after extraction.

    @STEVEusaPA

    Thanks. Not sure if the lines are steel all the way back to the tank, the 2 nubs are the only exposed portion.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,523
    Options
    @dbldangertilt

    Unless the old lines rotted out underground and were replaced with copper outside then they are steel.

    Be cautious some of the really old jobs had the suction line coming out of the bottom of the old tanks. This became illegal at some point but used to be done When this was done those jobs were usually 1 pipe.

    That was common back in the 20s & 30s.