In ground oil line abandonment
dbldangertilt
Member Posts: 3
in Oil Heating
We removed our oil fired boiler and hydronic setup and are looking to eliminate the remaining components including the burner. Any recommendations on how to handle the oil feed and return lines? How do I cap them temporarily and/or permenantly?
Thanks
Thanks
0
Comments
-
Blow them out and make sure there is no residual oil in them at all, and then cap them at both ends.
What are you doing with the tank?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Take the check valve off before blowing it back.
There was an error rendering this rich post.
0 -
The assumptions I make, @STEVEusaPA ... sigh... I assumed they would disconnect right back the elbows... oh well.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Yes, what are you doing with the tank?0
-
Haven't decided on what to do with the inground 675 tank. Soil samples came back negative. Has about 170 gals left. Would prefer removal vs abandonment (slurry fill).
What caps are typically used for the lines? Trying to diy as much as possible.
0 -
I'd agree that removal of the tank is the best approach. Remove it, take soil samples of the sides of the pit, continue soil removal until the samples are all negative. I'd use threaded caps on the lines.
However... this is not really a diy job. That tank, even after you get it pumped out, is going to be heavy. Further, it's structural integrity is going to be questionable. There are companies that do this for a living and know what they are doing -- and, perhaps more important, carry insurance against problems during removal and down the line if contamination is suspected. Try contacting your public health people or environmental protection people for suggestions.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Whatever you do, unless you break out the concrete you're going to have 2 pipe stubs.dbldangertilt said:...What caps are typically used for the lines? Trying to diy as much as possible.
After you blow out the lines, you can unscrew both elbows and just put on some regular steel caps. Hard to tell by looking buy I think they are 1/2" or maybe 3/4". Is it steel pipe back to the tank?
If you get the tank dug out, they can probably get the supply/return removed all the way back to the house. If that's the case I'd just fill them with cement at the wall, then cut the concrete floor around them and get those lines cut below the floor and patched.
There was an error rendering this rich post.
0 -
@dbldangertilt
If one or both of those oil lines extend to the bottom of the tank and where you disconnect the lines is lower than the oil level in the tank you will likely get oil syphon to you when you disconnect the lines.
You will have to cut the lines at the high point or work fast0 -
Thanks. Yes I was going to contract out for tank removal but try to cap the lines in the meantime.Jamie Hall said:However... this is not really a diy job. That tank, even after you get it pumped out, is going to be heavy. Further, it's structural integrity is going to be questionable.
This is exactly what I think will happen having disconnected lines for repair/maintenance before. A heating oil company will extract the remaining oil for $350 less 50 cents per usable gallon likely leaving 3-5 inches of sludge. I assume we may still get oil in the lines after extraction.EBEBRATT-Ed said:
If one or both of those oil lines extend to the bottom of the tank and where you disconnect the lines is lower than the oil level in the tank you will likely get oil syphon to you when you disconnect the lines.
You will have to cut the lines at the high point or work fast
@STEVEusaPA
Thanks. Not sure if the lines are steel all the way back to the tank, the 2 nubs are the only exposed portion.0 -
@dbldangertilt
Unless the old lines rotted out underground and were replaced with copper outside then they are steel.
Be cautious some of the really old jobs had the suction line coming out of the bottom of the old tanks. This became illegal at some point but used to be done When this was done those jobs were usually 1 pipe.
That was common back in the 20s & 30s.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 374 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements